Author Topic: Detecting if the AirCon is running...  (Read 2704 times)

0 Members and 1 Guest are viewing this topic.

Offline toftatTopic starter

  • Newbie
  • Posts: 6
Detecting if the AirCon is running...
« on: August 11, 2010, 06:15:39 pm »
I would like to optimize the setting of the thermostats in my house (I have programmable ones) to do this I need to detect if the AirCon is running. The idea being that a better setting will end up with lower runtime

I can't connect directly to either the AirCon or the thermostat so I need to observe the effect of it running, to this end I have come up with 2 ideas and am hunting for more

1) measuring a thermal delta between the vent outlet and "somewhere else" in the room. Somewhere else probably being against the ceiling to make sure that there _is_ a delta

2) measuring airflow. I have successfully done this using an old processor fan and measuring the voltage coming from the motor during hurricanes but I suspect the vent output is not forceful enough to generate anything significant...

As this is a hobby project, cost is a significant consideration...

Thanks for any further ideas!
 

Offline Simon

  • Global Moderator
  • *****
  • Posts: 18201
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: Detecting if the AirCon is running...
« Reply #1 on: August 11, 2010, 06:44:03 pm »
so you simply want to know when the AC is running ? do you have access to any low DC voltages in the AC unit ? if you want to detect the differnce in air temp putting a sensor on the top or in front of the intake and one in front of the outlet will certainly get you your delta C
 

Offline tecman

  • Frequent Contributor
  • **
  • Posts: 444
  • Country: us
Re: Detecting if the AirCon is running...
« Reply #2 on: August 11, 2010, 10:32:42 pm »
1.  Clamp on current sensor on air handler or compressor circuit

2.  Temp sensor on vapor line

3.  Airflow "sail" switch

All are relatively simple and cheap to use.

paul
 

Offline XynxNet

  • Regular Contributor
  • *
  • Posts: 185
  • Country: de
Re: Detecting if the AirCon is running...
« Reply #3 on: August 12, 2010, 09:58:48 am »
4. You could put a hall sensor near your aircondition fan.
 

Offline gbowne1

  • Contributor
  • Posts: 15
Re: Detecting if the AirCon is running...
« Reply #4 on: August 15, 2010, 05:45:53 am »
I don't know but you could set up a small PLC to control this.  AllenBradley Micrologix 1500's are nice for this.
You can set up all kinds of things on it, relays, sensors, switches, etc.

In my case, I'm adding a small GE FANUC 90-30 to my home control for the HVAC requirements of heating and cooling.

Greg
 


Share me

Digg  Facebook  SlashDot  Delicious  Technorati  Twitter  Google  Yahoo
Smf