Author Topic: Inverter Fail-Over relay circuit  (Read 601 times)
Offline JesterTopic starter
« on: April 24, 2019, 03:50:27 pm »
This is a AC transfer relay circuit that transfers from 120V MAINS to battery backed 120V inverter when the MAINS fail.
Do you think it will be safe and reliable?
Please delete
« Last Edit: April 30, 2019, 11:36:02 pm by Jester »
Offline Zero999
  • 0999
Re: Inverter Fail-Over relay circuit
« Reply #1 on: April 25, 2019, 03:04:50 pm »
No. You need a fullwave rectifier and a smoothing capacitor, to stop the relay from turning on and off at 60Hz or trying to.
I Googled the EE2-24NU.
https://www.mouser.co.uk/datasheet/2/212/KEM_R7002_EC2_EE2-1104574.pdf
Assuming I've got the correct data sheet, the coil resistance is 2k88, so you need a 12k 1W resistor.
I think this is a penny wise, pound poor solution and it would be better to use a 120VAC relay, even if it's more expensive and through hole.
Offline tecman
« Reply #2 on: April 25, 2019, 03:26:27 pm »
Another issue is the 00 uf capacitor on the relay coil.  This will delay the relay drop-out time resulting is a delay before the inverter power is applied.  Also the capacitor will cause a slow release which could cause some additional arcing as the contacts switch.  Minimize the capacitor sizing by using a full wave rectifier and only enough C to eliminate buzzing.
paul