I'm trying to control a borehole pump using a current switch. I have a ground source heat pump with an external heat exchanger with ground water as a heat source. Unfortunately there is no output from the heat pump telling when the compressor is running and thus needing ground water.
The compressor is internally VFD driven and I have a VFD driving the borehole pump. The latter VFD can except a on/off input e.g. as a 24 V/0 V and can source 24 V for that.
I thought it would be easy to put a clamp type current sensing to one of the three phases (400 V, 50 Hz) going to compressor VFD, but at least the first try didn't work.
First I used a clamp on True RMS multimeter and it showed less than 0.1 A when compressor was not running and about 1 A when it was running. The compressor takes about 0.9 kW at minimum load and can take up to about 4 kW.
Then I bought this (NPN-version)
https://www.crmagnetics.com/switches/ac-current/ac-voltage/cr9321and put one phase going to VFD through it. For testing I used a lab power set to 24 V and 0.06 A. With heat pump power, but compressor not running, the lab power showed 24 V and 0 A. When the compressor started it seems to take a while (10 s?) before the lab power started to show 2-3 V and 0.06 A. Later it went to 0.8 V and 0.06 A. But when the compressor stopped, it still showed 0.8 V and 0.06A. Even shutting the power input totally to the heat source pump didn't bring back 24 V.
What am I doing wrong?
I can't quite understand the specs of CR9321. I tried to ask them, but didn't get a helpful answer. I really can't understand what could be the difference between NPN and PNP models. Both have just two wires. What would it matter if the load is on negative or positive side? The CR9321 is floating and can only see the voltage and current between its wires.
Specs say that 0.35 A s rated full-on. It doesn't say anything about full-off. But having power switched off (from the electric cabinet of the house), should certainly qualify.
Is there an another current sensing switch known to work for this application?
Other option would be to use the 230 V used to power the circulation pump inside the heat pump. But that pump starts every now and then when the compressor is not running. Thus it would not be optimal.