I've been trying to use a solid state relay to switch a contactor, and have been getting very unreliable results. I was curious if I could get some help and insights.
In particular the SSR's love to stay latched onto the on state of the device. Regardless of the snubber used.
So you are saying, once turned on, the contactor does not release ? Does that happen 100% of the time ?
Do you have a scope to check the contactor coil waveform ?
The off state current may be enough to hold-in the contactor, the specs suggest the hold-in current is much lower than the peak pull-in current.
SCR SSR's need some current flow, to trigger the gates, so they never go to zero.
A power resistor across the contactor coil, would lower the voltage that sees in the off state.
Am I correct in my assessment that it is a dI/dt issue or is there something else at play?
It may be dV/dT more than dI/dT - inductor loads are not that nice, the SSR releases when current crosses zero, which is when mains is close to max, so there are high dV/dT effects.