Author Topic: How to calculate secondary volts/turn for a saturated mains transformer?  (Read 1103 times)

0 Members and 1 Guest are viewing this topic.

Offline Deactivated-1Topic starter

  • Frequent Contributor
  • **
  • Posts: 276
  • Country: 00
I'm planning to run an M470-50A UT13x17 54mm length core at 1.6Tesla, at which point it's well saturated. (stacking factor of around 4.1)
But at what tesla value can I expect the core to still excite the secondaries?

I have around 19.8VA draw from the secondaries. 1.7VA loss @ 1.6Tesla for the core. (0.385kg)
I'm expecting 0.22V/turn for the secondary voltages to be right. and my primary is 1000 turns, 80 ohms and powered with 237V 50Hz.
@ ~22VA the primary voltage would then drop to around 229V.

But how many turns/volt will I still have because of how low the permiability is at 1.6Tesla?

Here's the values for the core steel:
@ 50 Hz
J[mT] H[A/m] Ps[W/kg] μr[-]
1100 135 2.04 6502
1150 142 2.21 6423
1200 152 2.40 6285
1250 164 2.60 6059
1300 184 2.81 5625
1350 217 3.04 4941
1400 273 3.31 4080
1450 378 3.61 3049
1500 634 3.93 1882
1550 1155 4.21 1068
1600 2045 4.47 622
« Last Edit: January 01, 2024, 07:01:56 pm by ELS122 »
 

Offline CaptDon

  • Super Contributor
  • ***
  • Posts: 2376
  • Country: is
Re: How to calculate secondary volts/turn for a saturated mains transformer?
« Reply #1 on: January 01, 2024, 07:38:45 pm »
Why on earth would you want to push a mains powered transformer that far into saturation? No head room and insane amounts of magnetizing current and I2R losses with no benefits what so ever?
Collector and repairer of vintage and not so vintage electronic gadgets and test equipment. What's the difference between a pizza and a musician? A pizza can feed a family of four!! Classically trained guitarist. Sound engineer.
 

Offline johansen

  • Super Contributor
  • ***
  • Posts: 1246
Re: How to calculate secondary volts/turn for a saturated mains transformer?
« Reply #2 on: January 01, 2024, 08:15:55 pm »
Why on earth would you want to push a mains powered transformer that far into saturation? No head room and insane amounts of magnetizing current and I2R losses with no benefits what so ever?

the benefit is the power density of a transformer follows the flux density squared. -its just a trade off between no load losses and full load losses.

But how many turns/volt will I still have because of how low the permeability is at 1.6Tesla?

find a 24volt 40va control transformer from the nearest HVAC' companies dumpster, measure it. its pretty similar to what you're designing.
 

Offline Benta

  • Super Contributor
  • ***
  • Posts: 6591
  • Country: de
Re: How to calculate secondary volts/turn for a saturated mains transformer?
« Reply #3 on: January 01, 2024, 08:28:37 pm »
Secondary voltage will be the same, but you'll literally be running an air cored transformer. Immense magnetising current and not very efficient.
 

Offline Benta

  • Super Contributor
  • ***
  • Posts: 6591
  • Country: de
Re: How to calculate secondary volts/turn for a saturated mains transformer?
« Reply #4 on: January 01, 2024, 09:42:19 pm »
That's obvious. Primary-secondary coupling will also suffer. But the idea is so outlandish that I have no interest in providing detailed replies.
 

Offline johansen

  • Super Contributor
  • ***
  • Posts: 1246
Re: How to calculate secondary volts/turn for a saturated mains transformer?
« Reply #5 on: January 01, 2024, 09:56:27 pm »
I have a small transformer running at 1.4T, its an off the shelf 35VA 24vac transformer.

somehow they fit 650 turns of 28 gauge wire for the 120v primary at 19 ohms, and 150 turns of 22 gauge wire for the secondary at 1 ohm.

it consumes 3.8 watts at .110 amps at 110vac and a 3 turn secondary makes .5110 volts
it consumes 5.0 watts at .162 amps at 122.5 vac and 3 turn secondary makes .5653 volts.

the additional .050 amps times 19 ohms makes for 1 volt disappearing and this is appears to show up in a slight reduction of what the 3 turn secondary should produce.

my spreadsheet says my transformer weighs .44 kg of iron. i have to crank the volt amps per kilogram up to 45, to get a magnetizing current of .162amps.

the no load copper loss is supposed to be only 0.5 watts.

the core is welded with all the E's on one side, and it has generous holes drilled in the 4 corners, so its probably saturating in the corners. but the bulk of the core is at 1.4T flux density for the 19mm by 26mm core cross section.

hope this helps.

with a 22.5 ohm load the volts drop from 28.7 to 25.6 and my kill a watt meter says its pulling 40 watts out of the outlet at 0.90% power factor.
the problem being i only have 30 watts dumped in the load. -this is about 4 watts lost in the core and 6 watts of copper losses, for 75 to 80% efficiency.
« Last Edit: January 01, 2024, 10:53:55 pm by johansen »
 

Offline duak

  • Super Contributor
  • ***
  • Posts: 1048
  • Country: ca
Re: How to calculate secondary volts/turn for a saturated mains transformer?
« Reply #6 on: January 01, 2024, 10:33:07 pm »
Slipping a few turns of fine gauge wire tightly around the windings will allow you to measure the volts/turn with an oscilloscope. Please note that the secondary is still "excited" by the flux set up by the primary winding when the core is saturated.  However, in saturation the core cannot support much more flux and since the instantaneous voltage on the secondary is a function of the change in flux, the peak voltage will be limited.  You should see this with a scope as a flat-topped, distorted sine wave.

Are you trying to make a constant voltage (ie. voltage regulating) transformer?

Cheers,
 

Offline johansen

  • Super Contributor
  • ***
  • Posts: 1246
Re: How to calculate secondary volts/turn for a saturated mains transformer?
« Reply #7 on: January 01, 2024, 11:31:40 pm »
another crude test i did on a smaller 25va transformer of turns ratio 4.25:1 delivering 28.6 volts open circuit at 122v primary.

shorted the secondary and provided it 27.7 volts from another transformer. 1.31 amps flowing in the secondary.

according to the resistance of the primary, 44 ohms, and 4.25^2 *1.73 ohms for the secondary, which equals 31.5 ohms, i should have had 0.36 amps flowing in the primary and 1.56 amps in the secondary, instead i only had 1.3

« Last Edit: January 01, 2024, 11:35:59 pm by johansen »
 