Electronics > Projects, Designs, and Technical Stuff
KWh meter - is there such a thing as a non-contact one?
floobydust:
The utility industry uses capacitive voltage dividers. I have seen them on 240kV power lines to monitor voltage, instead of potential transformers (PT). It's much lower cost.
But at 120VAC, it's easiest to use a resistor divider.
There are single phase DIN rail mount energy meters for under $30 on eBay. Probably burn down your house unless it uses pass-through CT's, fused voltage sampling.
EEVblog:
Not commercially that I am aware of, apart from the clamp based ones, but I know someone working on a multi vector magnetometer based design for remote non-contact switch board current measurement.
Resolution isn't great and requires calibration, but it works. Can't measure voltage of course.
soldar:
You really need to measure (connect) voltage. Voltage variation, wave shape, reactive loads will all affect the measurement. You cannot just multiply current by an assumed voltage.
EEVblog:
--- Quote from: soldar on April 03, 2019, 09:59:29 am ---You really need to measure (connect) voltage. Voltage variation, wave shape, reactive loads will all affect the measurement. You cannot just multiply current by an assumed voltage.
--- End quote ---
Well, you can, it's just a matter of how much error you are willing to accept.
Our mains voltage for example doesn't vary by a huge amount, so multiple a fixed value by the RMS current and you are in the ballpark.
Zero999:
--- Quote from: EEVblog on April 03, 2019, 10:18:19 am ---
--- Quote from: soldar on April 03, 2019, 09:59:29 am ---You really need to measure (connect) voltage. Voltage variation, wave shape, reactive loads will all affect the measurement. You cannot just multiply current by an assumed voltage.
--- End quote ---
Well, you can, it's just a matter of how much error you are willing to accept.
Our mains voltage for example doesn't vary by a huge amount, so multiple a fixed value by the RMS current and you are in the ballpark.
--- End quote ---
But that will only give you apparent power, not true power. If you could obtain the phase of the sine wave by capacitive coupling, then you stand more of a chance.