mrpackethead:
Hi, I'm in the process of setting up some new workstations in our new workshop. ( horrah! space! )..  I'm going to have a goodly number of AC Sockets along the bench, as there is nothing worse than running out of places to plug stuff in.   

I'm able to put some individual RCD's in at the Workstation, and i'm contemplating if i put 6 or 20mA ones in.    6mA may trip and be annoying. 20mA may allow just enough current to seriously hurt or kill someone.       We do assemble items with AC power supplies, and sometimes have items 'open' while they are powered up.   

Thoughts?
capt bullshot:
Just read my signature  8)
Berni:
4mA

If a single device trips that then it is faulty,

The reason that the less sensitive RCDs are used is that they tend to supply an entire house. The leakage currents of everything adds up with the many devices plugged into it so it has to be more tolerant to not false trip. This is the reason why bathrooms in a lot of countries are required to have a dedicated RCD. It allows for the use of a more sensitive one by minimizing the amount of stuff connected.
Zero999:
Yes, use the lower tripping current. From memory, the leakage current should be below 1mA anyway.
Ice-Tea:
I got the lowest I could get (which is 10mA).

Rule of thumb is:

1 mA can be felt
10 mA you'll feel all day
100 mA: if it takes the scenic route you'll feel no more

I thought 2mA was permissible (think: EMI caps to earth and such). So if you're attaching several PSU's on a 4mA line you'll run out quickly.