[/quote]
Is there a line filter in front of the surge suppressor (CTD-1 module)? A line filter includes a small RC filter to snub small spikes and to filter out common-mode noise.
What is the device your protecting? Note from the CTD-1 module data sheet the intended application:
Application: This device provides a source of energy for circuit breakers and switch trip coil operation
during a loss of AC control voltage
This device is using a half wave rectifier, and not a full bridge rectifer used in most devices. a half wave recifier will have issues with high current applications.
Also note, this is a single channel shunt mode protector. It will not prevent damage from common mode surges, or other surge protectors that use three way surge protection. Consider if there is a common mode surge where line and neutral experience a common mode spike (ie both line and neutral have a 400V spike at the same time). Since the device has a earth ground, the MOV will do nothing and permit a high voltage differential between L-N and ground. The device will like pass the surge through it using the ground line.
Consider that other devices at the customer premises might include a three way shutmode suppresion circuit that diverts the surge to ground. Now the high side of the surge is the Earth ground and use Line-Neutral and return blowing your device from the ground. Consider that the average household\commerical ground line has about 6 ohms resistance, providing ample room for destruction.
Three way MOV surge protection:
[/quote]
There is no line filter ahead of this or any other device on the AC supply. The AC supply typically consists of a stepdown Control Power Transformer. It's primary side is connected to the switchgear's medium voltage bus ( 2400-38000 volts ), usually Line to Line. The secondary side is wired for 240/120. The gear is a giant steel box with a .25x2 inch ground bus traveling through. The ground references are attached to the ground bus. Resistance would be very low. There are other devices present that are much more sophisticated, the protective relays like the SEL brand. The CTD-2 does not have a ground reference. The relays do. Some relays have a chassis ground, safety ground, & a filter ground.
The device we are protecting varies greatly. Medium Voltage Switchgear is used as service entrance equipment for hospitals, large industral plants, etc.
The devices all utilize the primary voltage, say 13800. Lets say the load is a 12,000 HP air compressor. That section of gear would provide a protective relay ( customer's choice ) for the motor. The protective relay senses a problem has developed, maybe high temperature on a set of bearings. The relay then closes a normally open contact. This completes a trip circuit for the medium voltage circuit breaker, the CTD-2 supplies the DC voltage. Customers that are too cheep to maintain a battery rack use a capacitor trip device. Maybe they just think it is more "green". The trip current is 6 amperes peak. The shunt trip coil is energized for 34 milli-seconds. With the AC control off, the CTD-2 capacitor is discharged from 179VDC to 80VDC.
What do you consider a high current application ? For our switchgear that would be about 4000 amperes.