Author Topic: Power supply suggestions  (Read 818 times)
Offline Red_MicroTopic starter
« on: June 18, 2021, 02:39:51 am »
Is there a commercial solution for a Power Supply Input = 400VAC input (3 phase), Output = 36VDC, 2.2kW? From a design perspective, what topology is a fit for this requirement? Any literature is welcome.
Offline bob91343
Re: Power supply suggestions
« Reply #1 on: June 18, 2021, 03:03:15 am »
 I presume you want an old school solution.  A three phase transformer with appropriate rectifiers.
The details can vary a lot depending on your specific need, but a Y - to Y set of transformers with full wave rectifiers should do it, although the ripple requirements may mean some hefty capacitors.
See any textbook on AC circuits and/or transformers.
« Reply #2 on: June 19, 2021, 07:53:51 am »
Drop us a lot more detail first.
Is this a test fixture for occasional use, casual short term usage (low duty cycle) or 100% duty cycle 36VDC @ circa 60A?
What sort of spec do you need +-0.1VDC ok with a bit of ripple or do you need tight and a few mV and Linear/Low Ripple?
Why three phase? Can you do it with split phase 220V (assuming you are on 110V?) instead?
New or Secondhand?  eBay auction: #264893002059 just about bang on your rough spec. Several available in the USA it seems.
« Last Edit: June 19, 2021, 07:58:00 am by beanflying »
Offline sandalcandal
  • MOAR POWA!
« Reply #4 on: June 21, 2021, 03:21:34 pm »
Do you really need 3 phase for only 2.2kW?
Modern high efficiency designs would use a WBG totem-pole PFC into a high efficiency DC-DC converter, mostly LLC it seems like these days.
Here's a reference design in your ball park: https://www.infineon.com/cms/en/product/evaluation-boards/eval_3kw_50v_psu/
Disclosure: Involved in electric vehicle and energy storage system technologies
Offline penfold
« Reply #5 on: June 21, 2021, 07:53:39 pm »
They are not common. In a chassis mount unit, 2.2 kW doesn't really give much incentive to add the cost and space consumption of a three-phase front end. XP Power makes some three-phase units Like these but not at your voltage spec.
(assuming you need three-phase, say for avoiding unbalance on a small power system), you could perhaps connect three single-phase units so long as their outputs allow parallel operation.
For the front-end, PFC stage, you can use one single-phase PFC per phase if you have a neutral, a Vienna rectifier can be quite suitable (not entirely intuitive to control though) or a three-phase IGBT/MOSFET-bridge boost converter. The DCDC bulk power conversion part would probably be good with a phase-shifted bridge with probably a push-pull secondary can work well, relatively simple to design and easy to control... other approaches can be more efficient.