tapasxplore:
We are working to control the proportional solenoid valve, by changing the voltage across it. For this we are using PWM from the controller, thus changing the average current across the valve.

The controller (i.MX RT1060 from NXP) is capable to give up-to +3.3V. We are using TIP 122 NPN Darlington transistor to switch the voltage to 9V. Whenever we are changing the duty cycle from 95% to 100%, then only the valve is getting ON. If we are giving duty cycle is below 90% the valve is completely OFF.

We are giving 5KHZ PWM frequency, with 16 bit PWM resolution. The experiment result is mentioned below. Have a look at the sudden increase in the voltage (table attached) from the duty cycle 95% onward. We are getting controller flow, in between 95% to 99% only. If the circuit should work, if should work for the whole range.

Initially we have used base resistor of 390 ohm. We thought at lower duty cycle the voltage from the controller to the base of the transistor should be less. We decreased the resistor value from 390 to 190 and then to 47 ohm. Still did not get significant change across solenoid voltage at lower duty cycle. The flow vs duty cycle graph is not matching the datasheet.



mikerj:
Where is your freewheel diode?  Have you checked what voltage you are getting on the TIP122 collector when it switches off (with a scope, not a multimeter)?  A TIP122 is only rated to 100v, so there is a good chance you are exceeding that unless there is something built into the solenoid to clamp this.

tapasxplore:
Thanks, with the diode connected it is working fine.