An LC filter can be added between the switching circuit and solenoid so that it is driven with DC rather than low frequency PWM. This combines the efficiency of PWM with a linear drive signal.
Interestingly, the pulsed nature of the PWM signal is an advantage with proportional valves. This is why I said "frequency set low enough to act as dither to improve hysteresis response" above. The valves tend to have a certain amount of "stiction" if held in a single position for a while, so the manufacturers recommend that the PWM signal be of a low enough frequency to induce dither - thus causing the valve to mechanically move a bit. This improves response to small changes. Thus we don't want to use an LC filter, we actually
want the actuator to experience the "AC" of the PWM signal. The nonzero mass of the actuator obviously prevents it from responding to the electrical rise/fall time.
Also, for a bidirectional motor application, there are
two such proportional valves with two separate solenoids. You don't have a midpoint (such as 50% PWM duty cycle) and drive it up or down, you drive one coil from 0-100% for clockwise rotation and the other coil 0-100% for counterclockwise rotation. The two coils are never actuated at the same time.