So I had a need to fuse some 12V MPPT solar at 30 Amps
Fortunately, I very convenient had some spare spots on a fuse bank.
Less fortunately, they were normal size automotive blades, and those are not ideal for 30 Amps. One should not use them above 20 Amp, go to Maxi size instead.
And indeed, a test run with the battery empty and full sun so full 30Amp for 2 hours meant they got a tad too warm.
So I had the .... "briliant" ... idea of putting 2x 20 Amp fuses in parallel.
Also inspired because my own camper, an A-listed brand German Westfalia, did the same from factory with the battery-2-battery charger. Monkey see, monkey do.
Considerations
Pro:
- heat will spead over twice the area
- If one fuse is slightly off balance, it will get warmer, increase resistance, and thus throttle back in respect to the other (auto-leveling)
- If one goes, the other goes near instantly
- Variance means it probably is more similar to 2x15 rather then 2x20, so same 30 amps.
- Having two actually averages out fuse variance a little, the nominal value is higher (40 Amp), but a single 30 Amp might actually go higher then the averaged pair of 20 Amps
(Cable is 6mm2 so enough anyway)
Con:
- It just feels wrong.
Anyway, now the pair stays at 45 celcius, where before on a single 30 it went to 105 celcius (2 hours of 30Amp load)