I have a device that takes a 3phase 400VAC 16A input, and drives a range of "load" devices. The big loads primarily resistive (heating elements) but a few are inductive as they are small (250W) AC induction motors. Those loads are not all on at any given moment, and are controlled by logic, so any given load can be on at any given moment and viseversa. The Loads are between each line and neutral, and have been allocated to be as evenly spread as possible, ie the 3 big heaters are across L1->N, L2->N and L3->N. If all loads were on, then there would only be a small neutral current due to that balancing, but if the loads are unbalanced, then the neutral current will be around 16A.
Ok, so that's the setup, the question resides around what sort of AC power filter architecture i need to provide, primarily to prevent external noise coming into this unit and messing things up (loads are Thyristor controlled and therefore to some degree potentially noise sensitive). The unit is going to be used in a high noise environment with regard to the AC supply (there can be up to 2MW of high performance prototype inverters / motor controllers running in the same room....)
I think:
1) The loads are unbalanced so that rules out a common mode type filter arrangement for the 3 phases
2) Neutral must be considered a power carrying conductor in this application
Schaffner sell what looks to be a suitable power filter for 3Ph + N asymmetric loads
http://www.farnell.com/datasheets/2188999.pdfOptions include simply buying that (expensive) filter device and including it inside our unit, or desiging our own power filter (we can reverse engineer the Schaffner part......

) to include on the power switching pcb that our unit already requires
Comments anyone?