ground connection on transformer secondary blowing fuse?
« on: July 05, 2013, 12:38:40 am »
So I have a isolation transformer, and I wish to add a switch to ground the transformer 2ndary so it is not floating. However if I do ground one of the transformer secondaries (to earth ground that is) the fuse just blows. Why is there a rush of current created by grounding one of the transformers secondaries?
 

Offline ftransformTopic starter

  • Frequent Contributor
  • **
  • Posts: 728
  • Country: 00
Re: ground connection on transformer secondary blowing fuse?
« Reply #1 on: July 05, 2013, 01:17:41 am »
oh fuck me, i am using a autoformer..................................................................................... I thought it was a 110:220V transformer......................  :-DD
 

Offline IanB

  • Super Contributor
  • ***
  • Posts: 13125
  • Country: us
Re: ground connection on transformer secondary blowing fuse?
« Reply #2 on: July 05, 2013, 02:56:19 am »
Yes, 99.9% of step up/step down voltage converting "transformers" are autotransformers.
 

duskglow

  • Guest
Re: ground connection on transformer secondary blowing fuse?
« Reply #3 on: July 05, 2013, 03:28:58 am »
Correct me if I'm wrong, but that means it's not an isolation transformer either, right?
 

Offline IanB

  • Super Contributor
  • ***
  • Posts: 13125
  • Country: us
Re: ground connection on transformer secondary blowing fuse?
« Reply #4 on: July 05, 2013, 03:39:27 am »
No, absolutely not an isolation transformer. If you test the (unplugged) transformer with your meter you will find continuity between the input and output sides.
 