Varistors in three phase application
« on: July 10, 2020, 10:38:50 pm »
Usually in three phase applications I see varistors connected between phase to phase, or between phase to ground. In the picture below from a power supply reference design, the common node of the varistors is not connected anywhere. I would expect it to be ground, but they intentionally left the common point of the varistors floating. How are varistors protecting in this case?
 

Offline trobbins

  • Frequent Contributor
  • **
  • Posts: 826
  • Country: au
Re: Varistors in three phase application
« Reply #1 on: July 11, 2020, 03:59:16 am »
Look at it from the perspective of a phase-to-phase, and a phase-to-neutral overvoltage condition.  A MOV will only start to conduct once the instantaneous voltage across it exceeds the 1mA Vdc threshold (which has a significant tolerance).  So if a phase-to-phase voltage spikes above circa 1.2kV then the connected MOV's will start to conduct to suppress a further rise in voltage.  Similarly for a phase-neutral voltage spike.  It would likely be rare for more than one conduction path to occur - in which case the voltage of the floating star node would be forced to change somewhat.