UPS repair - Any suggestions?
« on: September 09, 2018, 05:15:55 pm »
Mini Guard Series UPS does not turn on.
It behaves as if it does not see the battery or the incoming AC mains.
Does anyone have any experience, or a schematic diagram?
The display shown below does not appear.
Only the backlight is on, while button is pressed.

« Last Edit: September 09, 2018, 05:19:25 pm by AndersJ »
"It should work"
R.N.Naidoo
 

Offline Dbn281977

  • Newbie
  • Posts: 1
Re: UPS repair - Any suggestions?
« Reply #1 on: September 09, 2018, 11:05:42 pm »
I have no experience on this brand but, the ones i do repair are very heavy duty units and 90% of them i repair, the fuses to the battery bank are blown ans several MOSFETs are bad usually a dead short. I replace them and the fuses , never had anymore problems with the unit. Hope that points you in the right direction.
 

Online Gregg

  • Super Contributor
  • ***
  • Posts: 1141
  • Country: us
Re: UPS repair - Any suggestions?
« Reply #2 on: September 10, 2018, 04:49:36 am »
It may not turn on unless it senses a minimum DC voltage on the battery bus.  This is to keep from bursting bad batteries that may not take a charge.  If the battery fuses are intact, check the connections; if a lead acid battery has leaked, the corrosion can creep up the wire under the insulation and ruin crimp connections and even bolted connections.
 