True i did forget to take in account that heat pumps move significantly more heat than they consume. But still a block of ice remains very cheep because its just water, all the cost is in the container around it and this is easily expandable. It's not uncommon to have water heaters that hold more than 100kg of water, so the size of such ice storage would not get unpracticaly large just to store one day worth of air conditioning cold.
As for storing heat energy for half a year to cover the summer and winter difference is not easy. This does reach unpracticaly large sizes to store enough of it. Since latent heat can't be used for this, it makes it even worse (Tho molten wax can store heat pretty efficently). If you really wanted to have an advantage in terms of heating/cooling the best solution is to have an underground house. The ground temperature only varies by a few degrees trough the year. Tho in most climates the average ground temperature is too low to be comfortable, but some insulation and the waste heat from all the electrical appliances could bring that up closer to comfortable. But building such a house is expensive and you end up living in a windowless basement so it's not that great of an idea.
Geothermal is also in most cases too cold to be directly useful, but even the cold groundwater in winter is still a much better source for feeding a heatpump rather than the freezing air outside, can work for air conditioning tho. Unless you end up on top of a hot geothermal spring, those are very useful for heating, but are rather rare.
Using the ground as thermal storage is not without side effects though. While you store heat during the summer you dry out the soil and in spring it will stay frozen for longer. This has an impact on what you are able to do with the land. I recently talked to a guy who is using this approach for heating his home during winter, it seems planting something on this patch of land is not a good idea any more.
Update on the investigation in to the commissioning event.
https://mobile.abc.net.au/news/2021-09-28/fire-at-tesla-giant-battery-project-near-geelong-investigation/100496688
Fire at Tesla giant battery project near Geelong was likely caused by coolant leak, investigation finds
[...]
An investigation conducted by Energy Safe Victoria found the "most likely" cause of the fire to be a coolant leak in the Megapack cooling system, which caused a short circuit that led to a fire in an electronic component.
[...]
ESV said several changes had since been made to prevent any future fires, including each Megapack cooling system being inspected for leaks before on-site testing, and the introduction of a new "battery module isolation loss" alarm to firmware.
As for what happened here, the Tesla battery pack designs are liquid cooled which should make them incredible tolerant to fire, as long as coolant is present (not even pumped, just sitting in and filling the coolant lines). Given this occurred during construction, my guess is that during commissioning there was some fault with coolant not being in the system whether that be insufficient or not at all filling the coolant or a coolant leak then during a commissioning load testing the pack with faulty coolant fill could have overheated and caught fire. The propagation testing only guard against limited individual cell failure, not a whole pack overheating.
Regardless, something went very wrong with the system/installation process.
I wouldn't SHOUT about your assumed vindication as your proposed fault path was not correct. We only see a sanitized snippet of what happened and why. It seems to me that far more than one 'fault' led to this event, given they only owned up to about 3-4 cascading faults.
https://esv.vic.gov.au/wp-content/uploads/2021/09/VBB_StatementOfFindings_FINAL_28Sep2021.pdf
Source:
https://esv.vic.gov.au/news/cooling-system-leak-led-to-victorian-big-battery-fire/
and
https://esv.vic.gov.au/wp-content/uploads/2021/09/VBB_StatementOfFindings_FINAL_28Sep2021.pdf
Root cause
The most likely root cause of the incident was a leak within the Megapack cooling system that caused a short circuit that led to a fire in an electronic component. This resulted in heating that led to a thermal runaway and fire in an adjacent battery compartment within one Megapack, which spread to an adjacent second Megapack.
The Megapack that caught fire had been in service for 13 hours before being switched into an off-line mode when it was no longer required as part of the commissioning process. This prevented the receipt of alarms at the control facility.
• A key lock was operated correctly to switch the Megapack to off-line service mode (which was no longer required for ongoing commissioning) but this caused:
o telemetry systems for monitoring the condition of the (now out of service) Megapack to shut down and so remove visibility of the developing event
o the battery cooling system to shut down
o the battery protection system to shut down, including the high voltage controller (HVC) that could have operated a pyrotechnic fuse to disconnect the faulty battery unit.
Conclusion
The incident was most likely initiated by a Megapack coolant leak. The absence of a number of monitoring and protection systems that would have been available had the initial Megapack not been subsequently switched to off-line service mode allowed the initial fault to go undetected and resulted in the total loss of two Megapacks.
The affected Megapacks failed safely despite total loss
ESV requires Tesla to provide the final results of its investigation (when available) into why the fire resulted
in the loss of a second Megapack and what it is to do to prevent that circumstance arising again.
"The affected Megapacks failed safely despite total loss"
I'm not sure I see how they "failed safely" when one of them caught on fire due a coolant fault?
https://esv.vic.gov.au/wp-content/uploads/2021/09/VBB_StatementOfFindings_FINAL_28Sep2021.pdf
"The affected Megapacks failed safely despite total loss"
I'm not sure I see how they "failed safely" when one of them caught on fire due a coolant fault?
Perhaps they mean that it only caught fire and didn't blow someone's head off. Dunno. Failed safely from what? It's no doubt worded so the lawyers and insurance ghouls don't go bonkers.
The big thing for me is given that this overheat occured AFTER the charging stopped, AND the pack was taken offline, what caused the heating that the cooling system had to cool down and couldn't because it was leaky? If no power incoming or outgoing, and the pack is "offline", nothing should be getting hot, surely?
And why isn't the monitoring and safety control done inside the megapack regardless of the remote connection?
The most likely root cause of the incident was a leak within the Megapack cooling system that caused a
short circuit that led to a fire in an electronic component.
What a bunch of bullshit.
"The supervisory control and data acquisition (SCADA) system for a Megapack took 24 hours to ‘map’ to the control system and provide full data functionality and oversight to operators. The Megapack that caught fire had been in service for 13 hours before being switched into an off-line mode when it was no longer required as part of the commissioning process. This prevented the receipt of alarms at the control facility."
You simply poll the status registers all the time, MODBUS works well. You never have datapoints taking 24 hours of magic, what is this fake excuse they had no visibility of the packs?
When I'm doing site commissioning, it's the whole system and alarms that are mapped, never partials.
The following actions have been put in place to prevent a recurrence of this incident.
[...]
*The high voltage controller (HVC) that operates the pyrotechnic fuse remains in service when the key lock is isolated.
The big thing for me is given that this overheat occured AFTER the charging stopped, AND the pack was taken offline, what caused the heating that the cooling system had to cool down and couldn't because it was leaky? If no power incoming or outgoing, and the pack is "offline", nothing should be getting hot, surely?
And why isn't the monitoring and safety control done inside the megapack regardless of the remote connection?https://esv.vic.gov.au/wp-content/uploads/2021/09/VBB_StatementOfFindings_FINAL_28Sep2021.pdfQuoteThe most likely root cause of the incident was a leak within the Megapack cooling system that caused a
short circuit that led to a fire in an electronic component.
Not lack of cooling - coolant leaking and shorting something
As for why the safety/monitoring systems got inactivated, I would presume there is some sort of deactivation or "off" state used for shipping so that the monitoring and safety systems don't deplete the batteries below 0% SoC and cause damage (or danger) during transport and storage. Perhaps this state was improperly reactivated or they don't have a proper "in-commission but inactive" mode?