Hi,

Is it possible to cause damages to measuring equipment (oscilloscope, spectrum analyzer etc) and computers, if I plug in a device with high powered motor such an air conditioner or home fan to the same wall socket where I have plugged in my instruments and computers.

Here I have a surge protector at the main distribution box of my home but there is no surge protector at this particular wall socket. And I'm not using a UPS for any of my instruments and computer.

Thank you.
 

Offline Faringdon

  • Super Contributor
  • ***
  • Posts: 1949
  • Country: gb
I would have thought only if its an old or poorly maintained, or damaged fan or aircon unit. Decent ones should have built in circuitry to stop them putting out spikes back to the mains.
If you are worried you can always plug in some transient protectors...eg, a board containg MOVs.......or say, a HV capacitor board at the  output of a FWB....these steps will have clamp any transients.

But you can always make a  "transient catcher".....use eg a 450V LR8 linear reg at the output of a FWB....it will blow at the slightest high mains transient.
Maybe just set it up powering a led at 1mA or so......then see , over time, if it blows. Obviously dont put a filter in front of it.
« Last Edit: December 06, 2021, 07:51:01 pm by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline NiHaoMike

  • Super Contributor
  • ***
  • Posts: 8973
  • Country: us
  • "Don't turn it on - Take it apart!"
    • Facebook Page
Not much difference between a motor and transformer as far as switching transients go, they're both inductive loads.
Cryptocurrency has taught me to love math and at the same time be baffled by it.

Cryptocurrency lesson 0: Altcoins and Bitcoin are not the same thing.
 

Offline james_s

  • Super Contributor
  • ***
  • Posts: 21611
  • Country: us
Unlikely. I'm not even really sure what "sensitive electronics" would be, properly designed equipment should be able to tolerate voltage sags and spikes that occur in a typical household or office environment without any issues.
 

Online David Hess

  • Super Contributor
  • ***
  • Posts: 16548
  • Country: us
  • DavidH
Is it possible to cause damages to measuring equipment (oscilloscope, spectrum analyzer etc) and computers, if I plug in a device with high powered motor such an air conditioner or home fan to the same wall socket where I have plugged in my instruments and computers.

It should not result in damage with good power supplies, but I have seen it happen.  In an industrial setting the usual solution is to use a separate dedicated circuit for heavy motor loads, but where that was not possible, an online UPS solved the problem.
« Last Edit: December 07, 2021, 04:26:38 am by David Hess »
 

Offline floobydust

  • Super Contributor
  • ***
  • Posts: 6927
  • Country: ca
I have seen equipment damaged from janitors coming in and cleaning at night time, they plug their vacuum cleaner into any outlet. The universal motor and brushes arcing seemed to cause it. Took me a while to figure out what was going on. Also, I think power bars and surge protectors have the MOV's on the input side, not the outlet-side where the offender is plugged in.
 

Offline james_s

  • Super Contributor
  • ***
  • Posts: 21611
  • Country: us
It shouldn't really matter where the MOVs are, within reason. As long as there is a relatively low impedance path between it and the load, any transient that is there will be clamped.
 

Offline floobydust

  • Super Contributor
  • ***
  • Posts: 6927
  • Country: ca
Many powerbars have differential and common-mode chokes, and MOV's on one or both sides. It depends on the price and brand.
pic taken from Isobar teardown and review scope traces look useless though.
 

Offline james_s

  • Super Contributor
  • ***
  • Posts: 21611
  • Country: us
I'm somewhat skeptical of the value of MOVs anyway, the clamping voltage is fairly high, and they fail silently, or they can fail such that they catch on fire. I have relatively clean power here and usually look for non-surge protecting power strips and I've removed the MOVs from most of my UPS's after seeing one of them melt down at work several years ago.
 

Offline electronic_guyTopic starter

  • Regular Contributor
  • *
  • Posts: 78
  • Country: us
Considering the risk associated with AC motors I rewired the power cables connected to the wall plugs to the separate RCCB in my home lab setup. I have installed separate earthing rod also for the lab taking some precuation since I wear an ESD wrist wrap with the ESD mat. The RCCB is powered from main distribution box where I have installed type 2 SPD. The AC motor (Air conditioner) is also powered from the same distribution box, but since any spike that comes due to AC motor now has to come to the ditribution box first, hence I assumed that SPD will discharge it before it goes to my lab setup RCCB to damage the instruments. I hope my reasoning is correct. I considered installing type 3 SPD with the lab setup RCCB, but I cannot find a one in local shops. Any ideas from you guys? Am I making a faulty assumption here ?
« Last Edit: December 07, 2021, 05:01:13 pm by electronic_guy »
 

Offline floobydust

  • Super Contributor
  • ***
  • Posts: 6927
  • Country: ca
If it's a raw A/C compressor motor and 2-pole contactor, that can make the nastiest local transients. I find there is generator action due to the motor's remanence and kick back due to the mechanical load when it switches off, the spike can be huge and even make it past the distribution panel. I had some sites that were problematic and used a Dranetz power quality analyzers to figure that out.

I found best is RC snubbers at the transient source, across the A/C's contactor contacts. MOV's would also work. It also gives longer life to the contactor (less arcing) and less stress for the motor's insulation, not dealing with a many kV spike.
 

Offline rpiloverbd

  • Regular Contributor
  • *
  • Posts: 157
  • Country: bd
Depends on how well those 'sensitive' electronic devices were made.
 