Author Topic: Solar roof tiles in 2024  (Read 3504 times)
Offline PCB.Wiz
Re: Solar roof tiles in 2024
« Reply #25 on: November 08, 2024, 08:39:53 am »
These kind of solar panels start to become common in the Netherlands for new houses. A big downside is fire safety. If there is a fire in the attic, the integrated solar panels make it next to impossible for the fire brigade to put the fire out. They basically have to use an excavator to tear the roof off.
Is there something specific to solar tiles with the fire issue? Surely any solar panels on a roof represent high voltages and high power as a safety hazard when there is an emergency.
The problem there is not solar panels are combustible, but that they severely compromised the fire rating with this installation.
Such houses have internal fire walls right up to the roof line, and normally a fire goes straight up, but with panels mounted like that, flames funnel sideways and ignite the next roof cavity.
Someone’s goofed there.
Offline Marco
« Reply #26 on: November 08, 2024, 09:46:58 am »
It's not like flames push ceramic tiles to the side, let alone standing seam metal roofs, they make a hole.
Offline coppiceTopic starter
« Reply #27 on: November 08, 2024, 12:50:55 pm »
Nobody mentioned combustibility, although nctnico's suggestion of EPDM might be an issue there. The problem is the panels are producing power, inhibiting the ability of the emergency services to take action, during daylight hours. Breakers don't help when you have to attack the panels themselves, to get them out of your way. Breakers are generally pretty useless in emergencies anyway, as the responders won't know where they are.
Whether you have ceramic tiles, ceramic and solar layered tiles, or ceramic tiles with secondary panels doesn't seem like its going to change the combustibility issues all that much. Very little of the solar kit's content is things like combustible insulation. When I see the remnants of a house fire the roof generally looks like it remained in place until the rafters burned through to the point of the roof collapsing inwards. I can't see any kind of panel changing that much.
Offline Marco
« Reply #28 on: November 08, 2024, 01:17:41 pm »
Given the large increase in high voltage fires they have to deal with, I think my suggestion of conductive suits is pretty reasonable. It's relatively light weight compared to the rest of their suit, just needs a bit of care connecting all the parts.
Offline nctnico
« Reply #29 on: November 08, 2024, 02:44:21 pm »
Back in 2018 Fraunhofer did research into fire safety of integrated solar panels and found that these -at that time- posed a 20 times higher chance of causing a fire for various reasons. The lesson to take away from that is that integrating solar panels in a roof requires a complete re-design and different mindset of roof structures. I believe it can be done safe and way better compared to retrofitting panels which are not really intended for use on roofs to begin with. But somebody needs to design it that way and proof the design is safe.
« Reply #30 on: November 08, 2024, 02:50:49 pm »
I presume the risk is mostly around connection quality, so many small panels (tiles) might be much riskier than a small number of large ones.