Basically that UK houses typically have high-current single phase supplies. This is not really a very good idea, but the vast majority of domestic supplies, old and new, are single phase.
Ohh, wow...
...
This picture shows the road-side cabinet where my house is connected, they had to upgrade it to find space.
The main distribution cable in+out 4x150mm² go on the unfused blue clamps.
Usually the distribution is run in a sort of two-string zig-zag pattern along a residental road, this allows them to isolate one or two of these cabinets, while keeping power on the rest of the road. The unconnected cable on the right is one such fused "diagonal" connection, probably 4x100mm².
The white plugins hold three fuses or six fuses, and supply one or two cables.
The "drop" cables to the nearby installations are 4x6mm²
Because our house is 200m from this cabinet, they ran a 4x75mm² to another cabinet about halfway, that holds our 25A "mast-fuse" and the cable from there is 4x16mm².
One benefit of this system, is that the fire-brigade can pull the fuses when a house is on fire.
That's a neat system - assuming the cabinets are physically secure against vandals, vehicle strikes, Copper thieves etc!
The fire-brigade access is very useful.
Now I understand why the UK plugs have built in fuses!
As Monkeh says, irrelevant, too far down stream of the house breakers (it's there to protect the appliance cable), but I suspect that it wasn't a serious comment.
The detail which makes my hair stand on end is that the customers feed cable is only fused by the substation fuse.
Yes, I agree with you on that one, it
is a concern. The house feed cable, of smaller conductor area than the street cable isn't appropriately fused. The cable, whilst buried for most of its length, in older properties does come up through the house foundations and is exposed to some extent before entering the fused service head. In these properties, this entry is often under the stairs - a primary escape route.
Taking your 'plug fuse' comment as an example, there would, in all other circumstances, under the IEE wiring regs, be a protective device of appropriate rating to protect the house feed cable.
Electricity distribution companies are unfortunately a rule unto themselves. Whilst current edition wiring regs require things like non-combustible consumer units to reduce fire risk, they are not required to follow them (they have their own codes of practice) and
continue to install plastic cased service heads, isolators and meters new-builds (and upgrades - as my previous photo). They are, however, now brought up into a plastic cabinet built into the outer wall of the building. This houses the service head, meter and hopefully an isolator switch, with the connection to the customer's consumer unit inside the property via 25mm
2 double insulated tails. This should mean that any supply related fire should occur only on the outside of the building.
I don't believe that the supplier equipment is a significant cause of domestic fires (as badly installed (loose connections) older plastic consumer units can be. I think this is probably due to careful installation, but the small risk is there.