Author Topic: Correct location of fuse(s) in parallel solar panel connection  (Read 3187 times)

0 Members and 1 Guest are viewing this topic.

Offline abhishekkumar1902Topic starter

  • Regular Contributor
  • *
  • Posts: 53
  • Country: in
I have four 150 watt Solar panels which I am planning to connect in parallel to increase the current output. The spec of the panels are:
Nominal Maximum Power (Pm)            150Watts/12V
Open Circuit Voltage (Voc)                  22.50V
Short Circuit Current (Isc)                   8.81A
Voltage at Maximum Power (Vmp)       17.96V
Current at Maximum Power (Imp)        8.36A
Maximum System Voltage                   1000V
Link: https://www.microtekdirect.com/product/microtek-pv-module-150w/

I am just a bit confused where the location of fuse should be.

Of all the panels, should I wire all the positives and negatives respectively first, and then just drop a single fuse (may be of 35A/40A) in between the charge controller and this parallel panel connection. Or should I first drop a fuse for each panel first before making a parallel connection and then connecting it to the charge controller?, thus requiring one fuse per panel.

I also wanted to know what should be the amp rating of the fuse in each of the case mentioned above?
« Last Edit: May 30, 2018, 11:27:06 am by abhishekkumar1902 »
 

Offline fourtytwo42

  • Super Contributor
  • ***
  • Posts: 1185
  • Country: gb
  • Interested in all things green/ECO NOT political
Re: Correct location of fuse(s) in parallel solar panel connection
« Reply #1 on: May 30, 2018, 10:48:46 am »
PV equipment generally (panels, cables & connectors) are not designed to support more than two panels in parallel.
Perhaps you could use a series/parrallel connection ?
 

Offline abhishekkumar1902Topic starter

  • Regular Contributor
  • *
  • Posts: 53
  • Country: in
Re: Correct location of fuse(s) in parallel solar panel connection
« Reply #2 on: May 30, 2018, 11:26:11 am »
"PV equipment generally (panels, cables & connectors) are not designed to support more than two panels in parallel.", What? Why? Are u kidding me?
« Last Edit: May 30, 2018, 11:33:21 am by abhishekkumar1902 »
 

Offline fourtytwo42

  • Super Contributor
  • ***
  • Posts: 1185
  • Country: gb
  • Interested in all things green/ECO NOT political
Re: Correct location of fuse(s) in parallel solar panel connection
« Reply #3 on: May 30, 2018, 12:22:20 pm »
The cables and connector current rating is one reason, another is the reverse current rating of panels should they become shaded and several others. The vast bulk of panels are installed as series strings and that is the connection method assumed by the standard equipment, if you want to do something completely different it is up to you to make allowances.
I would suggest for example the use of Schottky diodes in series with each panel to limit fault currents and the use of higher rated cables and connectors as apropriate.
« Last Edit: May 30, 2018, 12:25:35 pm by fourtytwo42 »
 

Offline abhishekkumar1902Topic starter

  • Regular Contributor
  • *
  • Posts: 53
  • Country: in
Re: Correct location of fuse(s) in parallel solar panel connection
« Reply #4 on: May 30, 2018, 02:04:44 pm »
What happens if I don't install a blocking diode for each panel provided:
1.) Each panel had a bypass diode installed
2.) All the panels are in sun with no shading
 

Offline fourtytwo42

  • Super Contributor
  • ***
  • Posts: 1185
  • Country: gb
  • Interested in all things green/ECO NOT political
Re: Correct location of fuse(s) in parallel solar panel connection
« Reply #5 on: May 30, 2018, 06:24:08 pm »
What happens if you stick fingers in a power socket  :-DD
I probably should not have said that but power systems including PV are designed for safe operation.
« Last Edit: May 30, 2018, 06:26:46 pm by fourtytwo42 »
 

Offline abhishekkumar1902Topic starter

  • Regular Contributor
  • *
  • Posts: 53
  • Country: in
Re: Correct location of fuse(s) in parallel solar panel connection
« Reply #6 on: May 31, 2018, 06:25:25 am »
In a parallel connection, is there a way to get away with the blocking diode for each panel as they add a little voltage loss?
 

Offline fourtytwo42

  • Super Contributor
  • ***
  • Posts: 1185
  • Country: gb
  • Interested in all things green/ECO NOT political
Re: Correct location of fuse(s) in parallel solar panel connection
« Reply #7 on: May 31, 2018, 07:46:50 am »
It's a bit pointless asking for advice if your responce is to ask why you should take it!
 