Current sensing in an EV wall box
« on: August 15, 2021, 11:39:47 am »
EV wall box


Is it true, there is a need to do the following sensing?

1....Live current measurement (using CT torroid round the live)...this is AC current sesnsing
2....Live/Neutral current imbalance (using CT torroid round live and neutral). This is AC current sensing
3.....AC current in the CPC..using CT torroid round the CPC wire.

What DC current is needed to be measured, for protection purposes?....eg a DC current level in the live line?, DC current in the CPC?......are Hall sensors used to detect the DC level?
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #1 on: August 15, 2021, 12:28:05 pm »
Give it up Treez. You can't design an EV charger based on Youtube tear-downs. :palm:

Your employer needs to fork out for the standards, and you need to study them! |O


EDIT: As has already been said, the Rolec is one of the oldest chargers (or should I say, charging points) and requires external PEN fault protection, adding to material and installation costs and making it less popular with installers.
« Last Edit: August 15, 2021, 12:47:30 pm by Gyro »
Best Regards, Chris
 
The following users thanked this post: fourtytwo42, Faringdon

Offline f4eru

  • Super Contributor
  • ***
  • Posts: 1093
  • Country: 00
    • Chargehanger
Re: Current sensing in an EV wall box
« Reply #2 on: August 15, 2021, 04:48:31 pm »
making it less popular with installers.
making it less popular with installers in the UK.
PEN protection is not needed in other countries, due to TT earthing (or other schemes not using PEN).
« Last Edit: August 15, 2021, 04:58:53 pm by f4eru »
 
The following users thanked this post: Gyro, Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #3 on: August 15, 2021, 07:53:36 pm »
Thanks, the thing is, that DC current in the CT primary may saturate it, and mean its not effectively there.
Also, as you know, a CT cant measure DC current, so a Hall sensor must be used to sense the DC, but i dont hear details of hall sensors in these wall boxes.

What is the DC level in live and neutral under which the live/neutral imbalance CT is still required to work under.?....ie, without saturating the CT?
I presume that this gets addressed by just using a CT much bigger than would normally be needed?
« Last Edit: August 15, 2021, 07:55:57 pm by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #4 on: August 15, 2021, 09:45:11 pm »
Thanks, the thing is, that DC current in the CT primary may saturate it, and mean its not effectively there.
Also, as you know, a CT cant measure DC current, so a Hall sensor must be used to sense the DC, but i dont hear details of hall sensors in these wall boxes.

What is the DC level in live and neutral under which the live/neutral imbalance CT is still required to work under.?....ie, without saturating the CT?
I presume that this gets addressed by just using a CT much bigger than would normally be needed?

You don't appear to even have the knowledge or attention span to follow images and verbal commentary of the 13 minute video that you linked then! Either that or you only watched the first few minutes. If you can't follow a fairly layman description like that then there is no chance for you to safely start to develop such a product.

I really cannot believe that you can't see what's right in front of your eyes (or listen to what is being said on the video). You have to be trolling us.  I'm sorry, but words fail me! >:(
Best Regards, Chris
 
The following users thanked this post: fourtytwo42, alexnoot, Faringdon

Online mikeselectricstuff

  • Super Contributor
  • ***
  • Posts: 13748
  • Country: gb
    • Mike's Electric Stuff
Re: Current sensing in an EV wall box
« Reply #5 on: August 15, 2021, 10:45:23 pm »
Quote
1....Live current measurement (using CT torroid round the live)...this is AC current sesnsing
Not actually necessary, though some EVSEs measure AC current for information, apps etc. It could potentially be used to detect if the car is drawing more than it has been told is available, but this is a fairly unlikely situation, and would usually be covered by the circuit breaker feeding the unit
Quote
2....Live/Neutral current imbalance (using CT torroid round live and neutral). This is AC current sensing
Yes
Quote
3.....AC current in the CPC..using CT torroid round the CPC wire.
Not usually as (2) handles this.
Quote
What DC current is needed to be measured, for protection purposes?....eg a DC current level in the live line?, DC current in the CPC?.....
Neither - DC common-mode /leakage current on L & N. The video is incorrect, or at least unclear in this aspect, but then they are only electricians...
Quote
are Hall sensors used to detect the DC level?
Hall sensors are probably not sensitive enough. One sensor I took apart uses a fluxgate ( core saturation) type method, others might use GMR sensors.

« Last Edit: August 15, 2021, 10:51:57 pm by mikeselectricstuff »
Youtube channel:Taking wierd stuff apart. Very apart.
Mike's Electric Stuff: High voltage, vintage electronics etc.
Day Job: Mostly LEDs
 
The following users thanked this post: Faringdon

Offline NiHaoMike

  • Super Contributor
  • ***
  • Posts: 9018
  • Country: us
  • "Don't turn it on - Take it apart!"
    • Facebook Page
Re: Current sensing in an EV wall box
« Reply #6 on: August 16, 2021, 01:54:59 am »
Since a DC ground fault is most likely to involve the car chassis, add a sense resistor with bypass diodes in series with the ground line. Now it would be easy to detect a small DC leakage current.
Cryptocurrency has taught me to love math and at the same time be baffled by it.

Cryptocurrency lesson 0: Altcoins and Bitcoin are not the same thing.
 
The following users thanked this post: Faringdon

Offline uer166

  • Frequent Contributor
  • **
  • Posts: 893
  • Country: us
Re: Current sensing in an EV wall box
« Reply #7 on: August 16, 2021, 04:27:57 am »
Since a DC ground fault is most likely to involve the car chassis, add a sense resistor with bypass diodes in series with the ground line. Now it would be easy to detect a small DC leakage current.

God. We already went through this, please don't give advice unless you read the relevant standards. This is not how it's done and this will not be compliant. If it was that easy you wouldn't see everyone use some form of a overly complicated fluxgate sense. I guess who cares, it'll be interesting to see the train wreck of a product.
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #8 on: August 16, 2021, 06:54:40 am »
Quote
You don't appear to even have the knowledge or attention span to follow images and verbal commentary of the 13 minute video that you linked then! Either that or you only watched the first few minutes. If you can't follow a fairly layman description like that then there is no chance for you to safely start to develop such a product.
Thanks, yes,.....it took   me ages to find that video.....hours and hours of searching...the only video that gives any significant  info about the standards.

The problem is, it doesnt tell if its necessary to detect a DC current in the CPC?

Also, it doesnt tell  under what DC current level the RCD must be able to work up to ?(as you know, above a certain DC current level and the RCD wont work as it will be saturated)

Also, it doesnt tell  if the CPC AC current has to be detected, and what is the trip level?

We payed money for the EV standards...on the web....but they took our money and ran.

Also,can you get round the DC>6mA problem by just having a very large CT torroid RCD?....so it wont saturate on 6mA DC?...What DC current is it allowed to saturate at? (if you dont also have a residual dc current detector)?



« Last Edit: August 16, 2021, 07:08:25 am by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #9 on: August 16, 2021, 08:18:18 am »
Since a DC ground fault is most likely to involve the car chassis, add a sense resistor with bypass diodes in series with the ground line. Now it would be easy to detect a small DC leakage current.

God. We already went through this, please don't give advice unless you read the relevant standards. This is not how it's done and this will not be compliant. If it was that easy you wouldn't see everyone use some form of a overly complicated fluxgate sense. I guess who cares, it'll be interesting to see the train wreck of a product.

This is all just prolonging the agony. It's 'don't try to design the product without reading the relevant standards'! The train wreck stage is going to be far too late in terms of financial investment (presumably somebody is intending to spend money trying to manufacture it) and safety.
Best Regards, Chris
 
The following users thanked this post: uer166, fourtytwo42, Faringdon

Online mikeselectricstuff

  • Super Contributor
  • ***
  • Posts: 13748
  • Country: gb
    • Mike's Electric Stuff
Re: Current sensing in an EV wall box
« Reply #10 on: August 16, 2021, 08:30:02 am »

We payed money for the EV standards...on the web....but they took our money and ran.
Who did ?
Quote
Also,can you get round the DC>6mA problem by just having a very large CT torroid RCD?....so it wont saturate on 6mA DC?...What DC current is it allowed to saturate at? (if you dont also have a residual dc current detector)?
No because you don't know what RCD protection may exist upstream - you may be sharing an RCD with other loads, so a DC leak current could prevent that RCD acting on faults in the other loads.
Youtube channel:Taking wierd stuff apart. Very apart.
Mike's Electric Stuff: High voltage, vintage electronics etc.
Day Job: Mostly LEDs
 
The following users thanked this post: Faringdon

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #11 on: August 16, 2021, 08:50:24 am »
Thanks, yes,.....it took   me ages to find that video.....hours and hours of searching...the only video that gives any significant  info about the standards.

If you think that is "significant info about the standards" then it is best that I refrain from further comment.

Quote
We payed money for the EV standards...on the web....but they took our money and ran.

You mean you got ripped off by some fake bootleg site in China or Russia over some too-cheap-to-be-real bootleg copy. Or is it just another lie, like "My Rolec EV charger wall box has stopped working....." (Direct quote)?

As for the rest of the stuff, it would be irresponsible for anyone who hasn't read the relevant standards to comment. It would be unprofessional to give you possibly inaccurate safety related advice.


My honest advice at this point would be to go on bended knee to your customer and ask them to fund the purchase of the standards. If they expect to make any significant profit from this product, and considering the amount of money they stand to loose at the moment, they may well consider it a worthwhile investment - assuming that they are not too annoyed that you didn't do that in the first place.
« Last Edit: August 16, 2021, 08:56:11 am by Gyro »
Best Regards, Chris
 
The following users thanked this post: fourtytwo42, alexnoot, Faringdon

Offline fourtytwo42

  • Super Contributor
  • ***
  • Posts: 1185
  • Country: gb
  • Interested in all things green/ECO NOT political
Re: Current sensing in an EV wall box
« Reply #12 on: August 16, 2021, 12:36:55 pm »
I agree with Gyro, IMOP  it really is about time the mods got off there asses and did something about this guy. The number of inane posts is stupefying BUT here once again we have someone with little or no knowledge trying to become involved in potentially dangerous technology with a view to making a product for public use.  By continuing to allow these posts this website could be construed as being complicit in some unfortunate persons death.
« Last Edit: August 16, 2021, 01:26:04 pm by fourtytwo42 »
 
The following users thanked this post: Faringdon

Offline voltsandjolts

  • Supporter
  • ****
  • Posts: 2300
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #13 on: August 16, 2021, 03:26:10 pm »
I get the impression that treez' workplace is something akin to Fawlty Towers (British sitcom).
That is of course, if it actually exists. These days I'm inclined to think that just like Basil Fawlty, treez is also a fictional character.
I mean, all this, can't be real. Thank me if I'm right treez.
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #14 on: August 16, 2021, 06:20:03 pm »
Thanks, will get  the  standards.
« Last Edit: September 09, 2021, 09:49:33 am by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2117
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: Current sensing in an EV wall box
« Reply #15 on: August 16, 2021, 06:26:45 pm »
Dear Mods, please please keep Faringdon/Treez on this forum. We all need a laugh now and again.



Free the Standards!!! Rock-on Faringdon
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 
The following users thanked this post: Faringdon

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: Current sensing in an EV wall box
« Reply #16 on: August 16, 2021, 06:34:32 pm »
For goodness sake Farringdon, either shut up or put up!



Information abounds: https://en.wikipedia.org/wiki/SAE_J1772

I could knock up a useable charger in a couple of hours given this information, granted may not be safe for the never never to occur event or be legal but I could get power into a car, or buy a chinese portable 16A or even 32A portable charging access device for little more than I can buy a plug with the cable on it and less than a Type 2 level 3 cable costs in the UK!

There is a shortage of work in all sectors in the UK, maybe time to look for another job?
 
The following users thanked this post: alexnoot, Faringdon

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: Current sensing in an EV wall box
« Reply #17 on: August 16, 2021, 06:35:45 pm »
Thanks, and i'm sure you  would all agree that we have a duty to share  safety standards with the third world countries, the ones who cannot afford standards, and who cannot afford to train enough engineers to sort out what is compliant and what is not....as such, we should, i am sure you would agree, be sharing safety related standards on the web, so that those in the third world countries can live more safely....our project is for a third world country....we gave them wind turbines etc, and streetlights, and now we give them chargers for their albeit simple electric vehicles....we struggle for resources, but we try our  best.

If it's a standard it's copyright! if you have to pay money for it then sharing is definitely illegal.
 
The following users thanked this post: Faringdon

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2117
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: Current sensing in an EV wall box
« Reply #18 on: August 16, 2021, 06:37:17 pm »
Thanks, and i'm sure you  would all agree that we have a duty to share  safety standards with the third world countries, the ones who cannot afford standards, and who cannot afford to train enough engineers to sort out what is compliant and what is not....as such, we should, i am sure you would agree, be sharing safety related standards on the web, so that those in the third world countries can live more safely....our project is for a third world country....we gave them wind turbines etc, and streetlights, and now we give them chargers for their albeit simple electric vehicles....we struggle for resources, but we try our  best.
I am trying to be humourous lest my previous comment is taken in the wrong way.

Are you suggesting that you are designing EVSE for a 3rd world country??
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 
The following users thanked this post: Faringdon

Online Bud

  • Super Contributor
  • ***
  • Posts: 6911
  • Country: ca
Re: Current sensing in an EV wall box
« Reply #19 on: August 16, 2021, 07:24:43 pm »
3rd world countries can afford having electric vehicles but can't afford buying a few pages of information ?  :-//
Facebook-free life and Rigol-free shack.
 
The following users thanked this post: Faringdon

Online Ian.M

  • Super Contributor
  • ***
  • Posts: 12860
Re: Current sensing in an EV wall box
« Reply #20 on: August 16, 2021, 07:47:07 pm »
Many leading third world countries *DO* make their safety standards (which are often closely based on or direct copies of UK/EU standards) publicly and freely available, so contractors have no excuse (or legal defense) for shoddy or unsafe design or workmanship.  However some third world countries are not so enlightened.  e.g. your typical African kleptocratic 'government' never seems to get the idea that to maximize the amount they can steal, they have to feed the 'Goose that Laid the Golden Eggs' rather than killing it!
« Last Edit: August 16, 2021, 08:39:23 pm by Ian.M »
 
The following users thanked this post: Faringdon

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #21 on: August 16, 2021, 08:31:53 pm »
Thanks, and i'm sure you  would all agree that we have a duty to share  safety standards with the third world countries, the ones who cannot afford standards, and who cannot afford to train enough engineers to sort out what is compliant and what is not....as such, we should, i am sure you would agree, be sharing safety related standards on the web, so that those in the third world countries can live more safely....our project is for a third world country....we gave them wind turbines etc, and streetlights, and now we give them chargers for their albeit simple electric vehicles....we struggle for resources, but we try our  best.

This tactic reminds me of a post in his rambling "Electronics products...where are they made/designed?" thread - the one in which he revealed that his friend was setting up a duplicate of his company in China to manufacture his British products  ??? ( https://www.eevblog.com/forum/chat/electronics-products-where-are-they-madedesigned/msg3609021/#msg3609021

Maybe Rolec are about to get a duplicate that they don't know about!

This post strikes me as having a very similar tone...

Quote
OK, thanks.
Please do not let us blame the Good Chinese People....it is Westerners who place the orders for work.

So is it the case now, that the only realistic course for a  british (insert any western country here)  electronics company, is to get set up, then secretly  start a duplicate company in China using a "puppet" director...make all your money from the Chinese company (design and manufacture) ...and stagnate the engineering in the british company as much as possible (because it doesnt make as much money as the chinese part)...but keep the british company ticking over so you have a presecence in the UK electronics market, and can meet customers in UK  etc...and get them transferred over to the chinese  company if possible?
Is this the way to go now in UK (insert western country here)?
Since Western company's must do this because this is the hand they have been dealt by their governments.
You do this or somebody else comes and does it for you?..and puts you out of business?

Our Treez Faringdon is quite the philanthropist when under pressure or his motives are questioned.
« Last Edit: August 16, 2021, 08:58:15 pm by Gyro »
Best Regards, Chris
 
The following users thanked this post: Faringdon

Offline f4eru

  • Super Contributor
  • ***
  • Posts: 1093
  • Country: 00
    • Chargehanger
Re: Current sensing in an EV wall box
« Reply #22 on: August 16, 2021, 09:43:11 pm »
Standards mandated by law should always be free to use.
Sometimes they are!
If not, feel free to copy them.
 
The following users thanked this post: Faringdon

Offline NiHaoMike

  • Super Contributor
  • ***
  • Posts: 9018
  • Country: us
  • "Don't turn it on - Take it apart!"
    • Facebook Page
Re: Current sensing in an EV wall box
« Reply #23 on: August 17, 2021, 01:55:29 am »
God. We already went through this, please don't give advice unless you read the relevant standards. This is not how it's done and this will not be compliant. If it was that easy you wouldn't see everyone use some form of a overly complicated fluxgate sense. I guess who cares, it'll be interesting to see the train wreck of a product.
Looking at the OpenEVSE project, it looks like they detect DC ground faults by injecting a signal to the ground fault sense transformer and checking that it returns at about the expected level. Cheaper than adding a current sense to the ground wire.
https://github.com/OpenEVSE/OpenEVSE_PLUS
Of which, it looks like the license allows commercial use under some conditions. Not sure how to satisfy the attribution part without giving the impression that it's an official OpenEVSE product or is endorsed by the OpenEVSE team.
Cryptocurrency has taught me to love math and at the same time be baffled by it.

Cryptocurrency lesson 0: Altcoins and Bitcoin are not the same thing.
 
The following users thanked this post: Faringdon

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: Current sensing in an EV wall box
« Reply #24 on: August 17, 2021, 07:31:36 am »
Standards mandated by law should always be free to use.
Sometimes they are!
If not, feel free to copy them.

Often standards are freely available. You have to purchase a copy of the UK wiring regs as an electrician, but it's sub £100 which is what? an hours work for an electrician and the book does need printing. Ultimately someone has to pay and the cost of a standard is the least thing you will pay for when starting on something requiring the standard.
 
The following users thanked this post: Faringdon

Online mikeselectricstuff

  • Super Contributor
  • ***
  • Posts: 13748
  • Country: gb
    • Mike's Electric Stuff
Re: Current sensing in an EV wall box
« Reply #25 on: August 17, 2021, 08:29:05 am »
Looking at the OpenEVSE project, it looks like they detect DC ground faults by injecting a signal to the ground fault sense transformer and checking that it returns at about the expected level. Cheaper than adding a current sense to the ground wire.
I think that is just for functional testing of the RCD, not DC detection.
Though I do wonder if you could add DC detection to a conventional CT sensor by injecting a known waveform and detecting asymmetry, effectively turning the sense core into a fluxgate sensor
Youtube channel:Taking wierd stuff apart. Very apart.
Mike's Electric Stuff: High voltage, vintage electronics etc.
Day Job: Mostly LEDs
 
The following users thanked this post: Faringdon

Offline uer166

  • Frequent Contributor
  • **
  • Posts: 893
  • Country: us
Re: Current sensing in an EV wall box
« Reply #26 on: August 17, 2021, 10:01:20 pm »
Looking at the OpenEVSE project, it looks like they detect DC ground faults by injecting a signal to the ground fault sense transformer and checking that it returns at about the expected level. Cheaper than adding a current sense to the ground wire.
I think that is just for functional testing of the RCD, not DC detection.
Though I do wonder if you could add DC detection to a conventional CT sensor by injecting a known waveform and detecting asymmetry, effectively turning the sense core into a fluxgate sensor

There's not much fundamental difference between a fluxgate core and a CT core. The fluxgate core is optimized to have a very square BH curve with low-ish coercivity, while a CT one has high permeability for high secondary inductance to reduce phase shift. If you do this, you might as well get the correct core for the job. Other things include a massive difference in turns, you have 2000 for CT but say 10-20 for a fluxgate excited secondary. A fluxgate core can generally be much smaller since secondary inductance is not well defined and irrelevant. The trade secrets are the drive waveforms, various filtering details, and the cores themselves.
 
The following users thanked this post: Faringdon

Offline voltsandjolts

  • Supporter
  • ****
  • Posts: 2300
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #27 on: August 18, 2021, 01:48:21 pm »
The OP shouldn't bother designing an EV wall charger.
It would be a waste of time, because the electric car revolution car never happen.

That is, according to forum member opampsmoker.
https://www.eevblog.com/forum/beginners/electric-vehicle-revolution-cannot-happen-its-proven-do-you-agree/

...and what do users treez, ocset, zenerbjt, opampsmoker, coffeefet, Faringdon have in common?
 
The following users thanked this post: Faringdon

Online coppice

  • Super Contributor
  • ***
  • Posts: 8647
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #28 on: August 18, 2021, 02:15:07 pm »
Though I do wonder if you could add DC detection to a conventional CT sensor by injecting a known waveform and detecting asymmetry, effectively turning the sense core into a fluxgate sensor
Fluxgate sounds like a scandal over measurement errors. Its not obvious to me why fluxgate sensors are not more widely used. There's nothing inherently costly about them, compared to the widely used sensors which have numerous limitations compared to a fluxgate - no DC measurement, saturation, etc.

GMR sensors are another technology which seems to be limited more by a lack of effort than by inherent limitations.
 
The following users thanked this post: Faringdon

Offline nightfire

  • Frequent Contributor
  • **
  • Posts: 585
  • Country: de
Re: Current sensing in an EV wall box
« Reply #29 on: August 18, 2021, 06:17:12 pm »
Detection of a small DC leakage current is (in germany) mandatory because a RCD in the feeding network can go "blind".

More specifically RCD Type A go into saturation at 6 mA DC, so if this occurs, they will not trip anymore at AC leakage currents exceeding the nominal/rated current.

To overcome this a DC sensing has to be present at charging stations or charging adapters to prevent this.
Alternatively one could use a RCD type B which allows for higher DC leakage currents that maybe originate from very powerful battery circuits.

Attention: Because of this fact, a RCD Type B is not allowed to be put behind a RCD type A in those or similar applications.
 
The following users thanked this post: Faringdon

Offline uer166

  • Frequent Contributor
  • **
  • Posts: 893
  • Country: us
Re: Current sensing in an EV wall box
« Reply #30 on: August 18, 2021, 06:55:27 pm »
Though I do wonder if you could add DC detection to a conventional CT sensor by injecting a known waveform and detecting asymmetry, effectively turning the sense core into a fluxgate sensor
Fluxgate sounds like a scandal over measurement errors. Its not obvious to me why fluxgate sensors are not more widely used. There's nothing inherently costly about them, compared to the widely used sensors which have numerous limitations compared to a fluxgate - no DC measurement, saturation, etc.

GMR sensors are another technology which seems to be limited more by a lack of effort than by inherent limitations.

It's obvious once you try to actually design and use now, they are a major pain in the ass because:
  • They need to inject a few 100mV common mode to work for the excitation, therefore:
  • Anything that prevents/shorts out that common mode voltage af a few kHz will prevent the fluxgate from operating, therefore:
  • They don't work when the output is not "floating" relative to the input. E.g. you can't just put one in the output of a buck converter because there are caps at the input and output that create a "shorted turn" shunting the common mode.
  • That same voltage injection creates massive conducted EMC problems unless you have big Y-caps at the input and you let the output (i.e. vehicle) bounce around at ~kHz at a few 100mV
  • If you don't want to have the above issues, you use 2 cores in series, where one is the sense, and the other is CM cancellation, now you need extremely well matched cores otherwise the physics don't work
  • Saturation is not magically a non-issue as you alluded, you need to design the drivers/sense specifically to counter the primary current to avoid saturation. If you fluxgate is open-loop (most 6mA DC detection are), then you have the exact same problem.

If you have an option to go with CT, go with CT every time!
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #31 on: August 25, 2021, 07:52:33 pm »
Thanks, can the ZCT409 CT be used as a fluxgate sensor.....?...or is it one anyway?

ZCT409
https://www.ctzentar.com/zero-phase-current-transformer-for-leakage-current-detection-zct409_p28.html

« Last Edit: September 09, 2021, 09:50:32 am by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: Current sensing in an EV wall box
« Reply #32 on: August 25, 2021, 08:40:32 pm »
Ask the manufacturer?
 
The following users thanked this post: Faringdon

Offline m98

  • Frequent Contributor
  • **
  • Posts: 615
  • Country: de
« Last Edit: August 25, 2021, 10:04:43 pm by m98 »
 
The following users thanked this post: Faringdon

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: Current sensing in an EV wall box
« Reply #34 on: August 26, 2021, 07:32:41 am »
Yep, there is only one source for standards. Obviously if you go somewhere dodgy that promises for a cheaper price, um, yea....
 

Online mikeselectricstuff

  • Super Contributor
  • ***
  • Posts: 13748
  • Country: gb
    • Mike's Electric Stuff
Re: Current sensing in an EV wall box
« Reply #35 on: August 26, 2021, 08:08:48 am »
Yep, there is only one source for standards. Obviously if you go somewhere dodgy that promises for a cheaper price, um, yea....
Actually there are multiple - you can buy from each country's standards body. Apparently Estonia is the cheapest.
Youtube channel:Taking wierd stuff apart. Very apart.
Mike's Electric Stuff: High voltage, vintage electronics etc.
Day Job: Mostly LEDs
 

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2117
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: Current sensing in an EV wall box
« Reply #36 on: August 26, 2021, 08:24:12 am »
Yep, there is only one source for standards. Obviously if you go somewhere dodgy that promises for a cheaper price, um, yea....
If the standard is in use in the EU, then each EU countries standards body (BSI in UK) can sell the standard.  They can sell it for whatever price they wish.
We use the Estonian standards agency as they typically 5-20% of the price of BSI.

61010-1:2010 from BSI £350 (members £175, membership is £207 upwards)
61010-1:2010 from EVS €31.80 incl. TAX (£27.20)

www.EVS.ee
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #37 on: August 26, 2021, 08:38:28 am »
Can you use a "non fluxgate CT" for Fluxgate type sensing?.....if so, is there an associated inaccuracy?....i mean, arent the secondaries very low inductance with fluxgate sensor CTs? (as kindly  mentioned here already).

Also, if you need to do both 6mA DC testing, and the AC testing for 30mA imbalance aswell...then doesnt it make sense to use the "fluxgate" type approach, to kill two birds with one stone?
'Perfection' is the enemy of 'perfectly satisfactory'
 

Online mikeselectricstuff

  • Super Contributor
  • ***
  • Posts: 13748
  • Country: gb
    • Mike's Electric Stuff
Re: Current sensing in an EV wall box
« Reply #38 on: August 26, 2021, 09:03:04 am »
Can you use a "non fluxgate CT" for Fluxgate type sensing?.....if so, is there an associated inaccuracy?....i mean, arent the secondaries very low inductance with fluxgate sensor CTs? (as kindly  mentioned here already).
if it isn't specified for that usage, you have no idea of the tolerances of the core
Quote
Also, if you need to do both 6mA DC testing, and the AC testing for 30mA imbalance aswell...then doesnt it make sense to use the "fluxgate" type approach, to kill two birds with one stone?
Yes it makes sense to use the same sensor for AC and DC.
ISTR reading somewhere that current standards dictate that the EVSE shouldn't (maybe even must not ?) do the AC RCD function, but instructions should specify that they are connected to a type A RCD at source. Not sure how accurate this is, or where it is specified, but apparently  at least one EVSE manufacturer (Anderson) has removed the AC RCD functionality from its unit.
Youtube channel:Taking wierd stuff apart. Very apart.
Mike's Electric Stuff: High voltage, vintage electronics etc.
Day Job: Mostly LEDs
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #39 on: August 26, 2021, 02:10:31 pm »
Quote
Yes it makes sense to use the same sensor for AC and DC.
ISTR reading somewhere that current standards dictate that the EVSE shouldn't (maybe even must not ?) do the AC RCD function, but instructions should specify that they are connected to a type A RCD at source. Not sure how accurate this is, or where it is specified, but apparently  at least one EVSE manufacturer (Anderson) has removed the AC RCD functionality from its unit.
Thanks,  thats interesting. In fact, i  have only recently found out that EV wall box's should not have a Type A RCD function, because  it would be blinded by a DC current level at 6mA or greater.
An EV wall box needs to have a type B RCD, which  trips out on 30mA of AC imbalance, but  doesnt get blinded by even 100mA of DC level in the mains.
So an EV wall box needs a type B RCD and a DC level sensor which can sense up to greater than 200mA DC.

This is quite a spec...do you know of  off-the-shelf devices that can do this?
Does it mean only fluxgate sensors, or Hall sensors can be used?...since any "Normal" CT would be blinded by the DC.
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2117
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: Current sensing in an EV wall box
« Reply #40 on: August 26, 2021, 03:26:33 pm »
EVSE needs (depending somewhat on market/spec) someway of measuring current draw. Monitor the current in both L & N legs with shunts, monitor the line voltage and process this with a micro to extract power, current, balance, DC, freq, etc..

Even if you only use the shunt(s) to detect DC fault conditions, still pretty low-cost.

Or look up how AC+DC clamp meters work (split iron core & hall effect), and build something like that.
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 
The following users thanked this post: Faringdon

Online mikeselectricstuff

  • Super Contributor
  • ***
  • Posts: 13748
  • Country: gb
    • Mike's Electric Stuff
Re: Current sensing in an EV wall box
« Reply #41 on: August 26, 2021, 04:14:40 pm »
Quote
Yes it makes sense to use the same sensor for AC and DC.
ISTR reading somewhere that current standards dictate that the EVSE shouldn't (maybe even must not ?) do the AC RCD function, but instructions should specify that they are connected to a type A RCD at source. Not sure how accurate this is, or where it is specified, but apparently  at least one EVSE manufacturer (Anderson) has removed the AC RCD functionality from its unit.
Thanks,  thats interesting. In fact, i  have only recently found out that EV wall box's should not have a Type A RCD function, because  it would be blinded by a DC current level at 6mA or greater.
That isn't the reason. a 6mA DC sensor could sense 30mA AC.
Quote
An EV wall box needs to have a type B RCD, which  trips out on 30mA of AC imbalance, but  doesnt get blinded by even 100mA of DC level in the mains.
Nope. A type B RCD trips on DC or AC imabalance.
Quote

So an EV wall box needs a type B RCD and a DC level sensor which can sense up to greater than 200mA DC.
:palm:
The Type B RCD IS the DC leakage sensor.
I have no clue where you got 200mA from, but am losing the will to care.


Youtube channel:Taking wierd stuff apart. Very apart.
Mike's Electric Stuff: High voltage, vintage electronics etc.
Day Job: Mostly LEDs
 
The following users thanked this post: fcb, Kean, uer166, Faringdon

Offline nightfire

  • Frequent Contributor
  • **
  • Posts: 585
  • Country: de
Re: Current sensing in an EV wall box
« Reply #42 on: August 26, 2021, 07:00:41 pm »
Quote
Yes it makes sense to use the same sensor for AC and DC.
ISTR reading somewhere that current standards dictate that the EVSE shouldn't (maybe even must not ?) do the AC RCD function, but instructions should specify that they are connected to a type A RCD at source. Not sure how accurate this is, or where it is specified, but apparently  at least one EVSE manufacturer (Anderson) has removed the AC RCD functionality from its unit.
Thanks,  thats interesting. In fact, i  have only recently found out that EV wall box's should not have a Type A RCD function, because  it would be blinded by a DC current level at 6mA or greater.
An EV wall box needs to have a type B RCD, which  trips out on 30mA of AC imbalance, but  doesnt get blinded by even 100mA of DC level in the mains.
So an EV wall box needs a type B RCD and a DC level sensor which can sense up to greater than 200mA DC.

This is quite a spec...do you know of  off-the-shelf devices that can do this?
Does it mean only fluxgate sensors, or Hall sensors can be used?...since any "Normal" CT would be blinded by the DC.

Just got out of my yearly training for refreshments of knowledge here in germany regarding EVSE. Focus on the checks for electrical safety in operation here in germany and german regulations. (VDE is used here)


In short: RCD type B is not always necessary. There has to be a RCD present with max 30 mA for person protection, AND there has to be some way in a 3-phase setup to detect DC  currents, because above 6mA a RCD type A (which might be in the main distribution) will go "blind".
In a brand wallbox we had available for testing, a standard RCM module was used for this in combination with a standard RCD type A you could get at every corner.

OR one could use one of those quite new RCD type A-EV, which combine a traditional RCD type A and DC 6mA sensing.
Of course, the more highend way would be to use an RCD type B, which might be better available. And depending on the testing equipment (here in germany regulations say that once a year in commercial enviroment a wallbox etc. has to be tested) a RCD type B might be easier to test because of preprogrammed values in testing equipment.

In fact, many wallboxes in germany use only an inbuilt RCD type A and a DC recognition of 6mA.

Word of warning: It is not allowed to mount a RCD type B behind a RCD type A- simply because the type B would tolerate much more DC current than type A can handle- and what would affect some possible other circuits that might reside on the same RCD.
 
The following users thanked this post: Faringdon

Offline NiHaoMike

  • Super Contributor
  • ***
  • Posts: 9018
  • Country: us
  • "Don't turn it on - Take it apart!"
    • Facebook Page
Re: Current sensing in an EV wall box
« Reply #43 on: August 27, 2021, 02:23:12 am »
Wouldn't it be possible to have the AC GFCI continuously self test itself by injecting a signal at a substantially different frequency from the mains frequency? If there's a DC ground fault enough to disable the GFCI, the signal won't come back.
Cryptocurrency has taught me to love math and at the same time be baffled by it.

Cryptocurrency lesson 0: Altcoins and Bitcoin are not the same thing.
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #44 on: August 27, 2021, 05:48:38 am »
Quote
That isn't the reason. a 6mA DC sensor could sense 30mA AC.
Thanks, what form would that take...a fluxgate sensor?

Also..
Some fluxgate sensor questions?
1....Can an RCD  fluxgate sensor be done with a standard CT with  a single coil? eg a torroid  through which the power conductor pair are meant to simply  traverse the aperture.
2....What makes a fluxgate sensor accurate?.....is it the feedback loop?
3....If a batch of fluxgate cores have different saturation  current levels, will they  not give different current readings?
4....If a batch of fluxgate cores have varying BH loop widths, then wont they give different current readings?
5....If a batch fo fluxgate cores are pulsed with different frequencies, then wont they give different current readings?
« Last Edit: August 28, 2021, 02:43:59 pm by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
EVSE fails RCD tests.....de-install it?
« Reply #45 on: August 28, 2021, 02:37:40 pm »
Hi,
Supposing an electrician installs an EVSE in a household premises.
then suppose it fails the RCD test.....eg it trips on <15mA of AC imbalance, or doesnt trip till Fault DC gets up to 10mA..etc etc etc...
Is the electrician likely to de-install it , even though he wont be payed to do so?
Or will he just check it charges the car, and whether it electrocutes him when he touches the car?...... and if it does this , then he takes th emoney and runs?.....who is ever going to find out ?

'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: EVSE fails RCD tests.....de-install it?
« Reply #46 on: August 28, 2021, 04:42:17 pm »
what does it matter to you? my electrician was sweating badly when he tested mine and got dodgy figures. it reported an insane earth path resistance that we both know was wrong. He then as randomly as he got a fail got a pass and put those figures down. You tell me, was he right or wrong? I am happy, I watched him and helped him install it and knew very well that the install was fine. The meter was one side of the wall and the charging point the other side, total cable length was no more than 2m.

There are rules beyond your original topic that govern the installs. So you get the design right, leave the electrician to get the install right and everyone is happy. There are people all over the place that break rules in all sorts of things. The idea is that there are sufficient checks in place to catch the persistent wrong doers.

Ultimately I could have put that charging access point in myself with no obligation to show a future tenant or buyer the install paperwork, then what? That is why your job apparently is to design a device so safe that even if mis-installed would protect itself, the car and people. Mine has cut out on an RCD fault.
 
The following users thanked this post: Faringdon

Offline floobydust

  • Super Contributor
  • ***
  • Posts: 7000
  • Country: ca
Re: EVSE fails RCD tests.....de-install it?
« Reply #47 on: August 28, 2021, 05:11:39 pm »
These kind of threads should get locked, IMHO.

Faringon, don't ask us questions about subverting electrical safety with your company's EVSE product.
EE's have ethics and morals in protecting the safety of the public. We cannot enable anything criminal and have a cup of tea discussion about the electrician's ethics catching it.

Your test fixture is late, will not work etc. etc. and better to bite the bullet and face that fact instead of cheating and rolling out untested or fake tested product to the marketplace.
In jail there will be plenty of time for reading about CT construction and design. The leakage current test exists for good reason.
 
The following users thanked this post: janoc, Gyro, Faringdon

Offline dmills

  • Super Contributor
  • ***
  • Posts: 2093
  • Country: gb
Re: EVSE fails RCD tests.....de-install it?
« Reply #48 on: August 28, 2021, 05:51:39 pm »
There used to be a guy who posted here about his inability to design small switched mode converters for street lighting that actually worked reliably, he was vaguely amusing.
It is less so when someone starts doing much the same thing with power levels that are actually both dangerous and are directly exposed to the public.

Seriously, the standards are not THAT expensive in the scheme of things, get them, design to reliably meet them, and get your product approved by a suitable test house as meeting them, then profit. 

I would expect a sparks to confirm that the feed to the equipment was correct, and it would be nice if they tested the load, but I don't particularly expect it, any more then I expect the guy running a three phase feed to my new welder to run a quick bead to check the welder under load doesn't take the RCD out.
 
The following users thanked this post: Faringdon

Offline floobydust

  • Super Contributor
  • ***
  • Posts: 7000
  • Country: ca
Re: EVSE fails RCD tests.....de-install it?
« Reply #49 on: August 28, 2021, 06:05:08 pm »
We've already told OP to purchase the safety standards, the answer is "We payed money for the EV standards...on the web....but they took our money and ran."
Any solution offered gets punted aside:
"Thanks, also i am wondering about.."
"the thing is, the datasheets dont tell you"
"Yes but we cant do this"
"OK thanks, i can't tell you any more, but if you know..."

But knowingly bypassing safety regs is a no-no and you might ask the executive for an opinion.
 
The following users thanked this post: Wolfram, Gyro, Faringdon

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: EVSE fails RCD tests.....de-install it?
« Reply #50 on: August 28, 2021, 06:12:36 pm »
what does it matter to you? my electrician was sweating badly when he tested mine and got dodgy figures. it reported an insane earth path resistance that we both know was wrong. He then as randomly as he got a fail got a pass and put those figures down. You tell me, was he right or wrong? I am happy, I watched him and helped him install it and knew very well that the install was fine. The meter was one side of the wall and the charging point the other side, total cable length was no more than 2m.

There are rules beyond your original topic that govern the installs. So you get the design right, leave the electrician to get the install right and everyone is happy. There are people all over the place that break rules in all sorts of things. The idea is that there are sufficient checks in place to catch the persistent wrong doers.

Ultimately I could have put that charging access point in myself with no obligation to show a future tenant or buyer the install paperwork, then what? That is why your job apparently is to design a device so safe that even if mis-installed would protect itself, the car and people. Mine has cut out on an RCD fault.

The difference is that you bought a hopefully legit charge point, and therefore had some reasonable confidence that the install was actually safe and acceptable!
Best Regards, Chris
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: EVSE fails RCD tests.....de-install it?
« Reply #51 on: August 28, 2021, 06:20:28 pm »
Quote
Mine has cut out on an RCD fault.
Thanks, thats interesting....the RCD is a bugbear for EVSE's.........if you buy offtheshelf you have to buy the RCD (30mA/6mA) and relay in one package, and it costs a fortune.....so people want to make them themselves...and designing a 30ma/6ma RCD needs a fluxgate and isnt a quick cheap job.

Do you know if its possible to buy a type B RCD (30ma/6ma)  which doesnt contain the relay/contactor?.....but rather just a signal for you to use to actuate a relay/contactor?....i am pretty sure such a thing doesnt exist on the market?
................-----------------------......................
Incidentally, what would you think if an EVSE tripped out on 10mA of AC imbalance (instead of 30mA)?......thats a standards fail!....even though its safer as it trips out on less current.
............---------------------....................
Also, is there any reason that you cant use a cheap type B RCD, with a cheap relay in it...but just use it to instigate  a signal to turn off a more high quality relay/contactor?
Cheap Type B RCD (£20)
https://www.toolstation.com/axiom-incomer-devices/p90500?store=I6&utm_source=googleshopping&utm_medium=feed&utm_campaign=googleshoppingfeed&mkwid=s_dc&pcrid=515847200330&pkw=&pmt=&gclid=Cj0KCQjwvaeJBhCvARIsABgTDM4osmCd5dA_6O6J_ZpILg38mJGsz5GgxGBm0qkjN-WYnVQY5aEzKKoaAqE7EALw_wcB&gclsrc=aw.ds
« Last Edit: August 28, 2021, 06:37:53 pm by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: EVSE fails RCD tests.....de-install it?
« Reply #52 on: August 28, 2021, 07:58:20 pm »
As most of us are not privy to the standards we can't answer what you do and don't need.

Your link does not clearly explain what type the RCD is, which is part of being cheap!

Get the standards, read them, understand them because they also will not tell you how to design something only what the end result must be. Note that meek words like "shall" and "should" in standards mean: "YOU MUST DO THIS OR YOUR SORRY ASS WILL WIND UP IN JAIL AND IT'S YOUR FUCKING PROBLEM TO WORK OUT HOW TO ACHIEVE THIS AND THEN DEMONSTRATE HOW IT ADHERES TO THE STANDARD, ELSE YOU GO TO THE AFFORE MENTIONED JAIL".

My house earthing appears weird. It is both connected to the neutral and the conduit from the substation. My electrician has suggested I contact the distribution network to get them to confirm which it should be. My neighbours house is the same.
 
The following users thanked this post: Faringdon

Offline dmills

  • Super Contributor
  • ***
  • Posts: 2093
  • Country: gb
Re: EVSE fails RCD tests.....de-install it?
« Reply #53 on: August 28, 2021, 10:48:46 pm »
No access to the standards, but fluxgate sensors for DC measurements like that seem to be an off the shelf Part, Kemet FG-R05-3A for one example among others.

In sufficient production volumes it is probably cheaper to do your own, but certification costs make this sort of thing a better buy in at more modest volumes.
I was actually not aware that fluxgate was an off the shelf technology, but it appears to have very much become a thing.

Seriously, this shit is just not that hard, I found that part in distribution in < 30 seconds.

In standardese "Shall" is usually mandatory to comply, "Should" and "May" are quality of implementation things, "Should" generally being stronger then "May", but there will probably be a bit at the start of the document which explains this.

Thing is, there are PLENTY of standards around street furniture and lighting and I know you have played in that space so this shit should not be anything new.
« Last Edit: August 28, 2021, 10:53:03 pm by dmills »
 
The following users thanked this post: Faringdon

Offline nightfire

  • Frequent Contributor
  • **
  • Posts: 585
  • Country: de
Re: EVSE fails RCD tests.....de-install it?
« Reply #54 on: August 29, 2021, 01:13:07 am »
Quote
Mine has cut out on an RCD fault.
Do you know if its possible to buy a type B RCD (30ma/6ma)  which doesnt contain the relay/contactor?.....but rather just a signal for you to use to actuate a relay/contactor?....i am pretty sure such a thing doesnt exist on the market?
................-----------------------......................
Incidentally, what would you think if an EVSE tripped out on 10mA of AC imbalance (instead of 30mA)?......thats a standards fail!....even though its safer as it trips out on less current.
............---------------------....................


RCD Type B per Definition does NOT trip at 6mA DC, because it
a) can and shall allow higher DC leakage currents
b) for this reason it is NOT allowed to put a RDC type B behind a RCD type A


Tripping due to imbalance:
A standard RCD is allowed to trip within 50% and 100% of rated currrent, this means a 30mA RCD (AC) is allowed to trip anywhere between 15mA and 30mA. In the factory it is usually produced to get off at something between 20mA and 25mA to allow for some tolerance to both sides.
To answer that question: A EVSE, where the RCD trips outside spec, is considered defective and should be returned to point of purchase. Period.

A RCD Type B has different ranges on DC leakage current: Here we are talking about 15mA to 60mA DC as normative standard.


For all those, that maybe want to dive deeper in RCD technologies: German company Doepke publishes the so called "Allstromfibel", which is also available in english.
https://www.doepke.de/en/services/downloads/
 
The following users thanked this post: Faringdon

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: EVSE fails RCD tests.....de-install it?
« Reply #55 on: August 29, 2021, 07:18:41 am »


In standardese "Shall" is usually mandatory to comply, "Should" and "May" are quality of implementation things, "Should" generally being stronger then "May", but there will probably be a bit at the start of the document which explains this.


I didn't know the words themselves had um, standardized meanings. But standards are not the law. This is where it's a bit of a mind screw. The beginning of the UK wiring regs standard (BS 7673:2018 - yes I bought a copy, because I felt like it, oh so not expensive at £80 quid) points out that the standard is not the law but laws may impose that these standards are followed or recommend them as best practice. Again, a meek sounding expression - best practice. But in legalese this means it's all shits and giggles about what you care to do until something goes wrong, THEN it is up to you to prove that you followed best practice. This effectively translates into, "just do it this way or else". And this is why installations are supposed to be spot checked at random.
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: EVSE fails RCD tests.....de-install it?
« Reply #56 on: August 29, 2021, 01:58:05 pm »
Quote
For all those, that maybe want to dive deeper in RCD technologies: German company Doepke publishes the so called "Allstromfibel", which is also available in english.
https://www.doepke.de/en/services/downloads/
Thanks, it would be good to know the cost of those, i beleive we have to email them?
'Perfection' is the enemy of 'perfectly satisfactory'
 

Online themadhippy

  • Super Contributor
  • ***
  • Posts: 2583
  • Country: gb
Re: EVSE fails RCD tests.....de-install it?
« Reply #57 on: August 29, 2021, 02:21:29 pm »
Quote
My house earthing appears weird. It is both connected to the neutral and the conduit from the substation
sounds like they've converted TNS to a TNC-S  at some point,what is unusual is conduit from the substation,plastic ducting yea,some type of armoured cable,yea,but never seen conduit on the suppliers side.
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: EVSE fails RCD tests.....de-install it?
« Reply #58 on: August 29, 2021, 02:31:32 pm »
Quote
but fluxgate sensors for DC measurements like that seem to be an off the shelf Part, Kemet FG-R05-3A for one example among others.
Thanks, that looks a great part, and for $50

BTW, i am still a bit baffled why a RCD trip at 5 or 10mA would be a fail of standards...surely if the standards  threshold is 15mA , and you trip at 5mA, then youre safer than the standards? I cant see how you could be jailed over this,  or even fined.
« Last Edit: August 29, 2021, 02:55:24 pm by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: EVSE fails RCD tests.....de-install it?
« Reply #59 on: August 29, 2021, 03:11:22 pm »
Quote
My house earthing appears weird. It is both connected to the neutral and the conduit from the substation
sounds like they've converted TNS to a TNC-S  at some point,what is unusual is conduit from the substation,plastic ducting yea,some type of armoured cable,yea,but never seen conduit on the suppliers side.

Well it is some sort of armoured cable I suspect as it's external braiding that has be twisted into a wire and bonded to the neutral. Yea it does the electricians head in.
 
The following users thanked this post: Faringdon

Offline Simon

  • Global Moderator
  • *****
  • Posts: 17816
  • Country: gb
  • Did that just blow up? No? might work after all !!
    • Simon's Electronics
Re: EVSE fails RCD tests.....de-install it?
« Reply #60 on: August 29, 2021, 03:20:08 pm »
Quote
BTW, i am still a bit baffled why a RCD trip at 5 or 10mA would be a fail of standards...surely if the standards  threshold is 15mA , and you trip at 5mA, then youre safer than the standards? I cant see how you could be jailed over this,  or even fined.

Oh FFS get a job stacking shelves in your nearest supermarket!

Who said you go to jail or get fined if it trips lower than the standard? Again unless YOU buy the standard YOU will never know, those of us here not trying our hands at designing car charger access points could not give a flying toss what a standard we do not need to buy says.

If an RCD is too sensitive it will start tripping out at random due to leakage currents!!!!! That will make your customers mighty pleased now wont it? Your company will go bust due to all the returns of goods that are unusable! If the earth and neutral are ultimately connected together don't you think that the capacitance between the live and the earth will cause some permanent leakage? especially where the usual flat cable is used in the UK with the earth wire locked between the live and neutral.

When I connected my parents house that we rented when I lived in italy where dodgy electrics abound to earth I actually got current passing through me, the whole of the leakage current in the house was passing through me as I held the earth wire in one hand and the water pipe that was I was about to bond it to.
 
The following users thanked this post: station240

Offline nightfire

  • Frequent Contributor
  • **
  • Posts: 585
  • Country: de
Re: EVSE fails RCD tests.....de-install it?
« Reply #61 on: August 29, 2021, 08:43:43 pm »
Quote
For all those, that maybe want to dive deeper in RCD technologies: German company Doepke publishes the so called "Allstromfibel", which is also available in english.
https://www.doepke.de/en/services/downloads/
Thanks, it would be good to know the cost of those, i beleive we have to email them?

Nope. Free to download.
 

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: EVSE fails RCD tests.....de-install it?
« Reply #62 on: August 30, 2021, 12:00:19 am »
Quote
If an RCD is too sensitive it will start tripping out at random due to leakage currents!!!!! That will make your customers mighty pleased now wont it? Your company will go bust due to all the returns of goods that are unusable! If the earth and neutral are ultimately connected together don't you think that the capacitance between the live and the earth will cause some permanent leakage? especially wh
Thnaks, this is interesting, i see your point, now an EV will be the only thing coming off that wallbox, and the leakage from the charger will be just that bit from the y caps....so were taking maybe 3mA max.........this wouldnt spuriously trip an RCD which tripped at 5mA  to 30mA.
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #63 on: August 30, 2021, 12:01:18 am »
Hi,
We wish to make a RCD for an EVSE single phase  “wall box”. We will use a simple CT for the 30mA  imbalance detection. This may get  “blinded” by any DC leaking  in either line or neutral.
Therefore, we will also have a second CT the same as the first one, but will constantly  also inject 30mA AC 50Hz   through its aperture with a  wire loop. As soon as this second CT does not detect the 30mA , then that means it has been “blinded” by a DC current flow in either line  or neutral, so therefore we turn off the relay.
(We will inject the 30mA with constantly alternating polarity.)
Would this pass regulations? Why not? It surely guarantees safety, and is far cheaper than offtheshelf RCDs for 30mA/6mA  which are £30 upwards.
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline nightfire

  • Frequent Contributor
  • **
  • Posts: 585
  • Country: de
Re: Current sensing in an EV wall box
« Reply #64 on: August 30, 2021, 12:25:09 am »
In a single-phase setup DC recognition is not used by many of those ICCB that are use to charge a car from an ordinary outlet.

Reason: During operation, DC currents cannot happen.

Depending on the stuff you want to do, it might not be necessary- here you would have to look it up in the applicable standards.

Other question: If you really need a 6mA DC detection, why is a ready-made RCM module no way? They are regularly used by some big brands in their 3-phase wallboxes, which are sold in germany... In those a standard RCD Type A is used and a dedicated RCM for 6mA DC recognition is coupled via relay to a circuit breaker to switch off the box upon detection.
Makes the setup modular and repairable.
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #65 on: August 30, 2021, 09:34:29 am »
Thanks, but those offtheshelf RCDs are upwards of 30 euros each.

With an EVSE, i am not sure if the standards require DC detection, or just an assurance that any DC fault current wont blind the RCD.?

I know the metrel EVSE testers actually do a test for DC leakage current, and if the EVSE doesnt trip at >6mA DC  than thats a fail, (or at least, a fail according to the metrel tester)....whether its a standards fail i dont know.?
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #66 on: August 30, 2021, 10:03:54 am »
REM  Loop indefinitely (buy standards, understand standards, implement according to standards)!
GOTO 10
« Last Edit: August 30, 2021, 10:05:47 am by Gyro »
Best Regards, Chris
 
The following users thanked this post: fcb, Kean, Faringdon

Online mikeselectricstuff

  • Super Contributor
  • ***
  • Posts: 13748
  • Country: gb
    • Mike's Electric Stuff
Re: EVSE fails RCD tests.....de-install it?
« Reply #67 on: August 30, 2021, 10:13:35 am »

Cheap Type B RCD (£20)
https://www.toolstation.com/axiom-incomer-devices/p90500?store=I6&utm_source=googleshopping&utm_medium=feed&utm_campaign=googleshoppingfeed&mkwid=s_dc&pcrid=515847200330&pkw=&pmt=&gclid=Cj0KCQjwvaeJBhCvARIsABgTDM4osmCd5dA_6O6J_ZpILg38mJGsz5GgxGBm0qkjN-WYnVQY5aEzKKoaAqE7EALw_wcB&gclsrc=aw.ds
That is not a type B

Type B's start at around £100

The type is indicated by these symbols. It can be confusing, especially with RCBOs as the same letters are used for RCD type and overcurrent time characteristic, which was a really dumb decision by somebody
Youtube channel:Taking wierd stuff apart. Very apart.
Mike's Electric Stuff: High voltage, vintage electronics etc.
Day Job: Mostly LEDs
 
The following users thanked this post: Faringdon

Online mikeselectricstuff

  • Super Contributor
  • ***
  • Posts: 13748
  • Country: gb
    • Mike's Electric Stuff
Re: Current sensing in an EV wall box
« Reply #68 on: August 30, 2021, 10:24:23 am »
With an EVSE, i am not sure if the standards require DC detection, or just an assurance that any DC fault current wont blind the RCD.?
Why are you not sure ? You have either read and understood the standards or you haven't. In the latter case you are just wasting yours and everyone else's time.
Standards are not always the easiest things to understand, but things like this are usually pretty well specified.
I only have access to BS62752, for in-cable level 2 EVSEs but I'd be surprised if the standard for fixed units is any different in this respect.
This states :
Quote
8.8.4 Operating characteristics with smooth d.c. residual current
The IC-CPD shall verify that smooth d.c. residual currents do not exceed the value of 6 mA
and ensure a break time according to Table 3 in case that this limit is exceeded.
Compliance is checked by the tests of 9.7.6
What's not to understand?
Youtube channel:Taking wierd stuff apart. Very apart.
Mike's Electric Stuff: High voltage, vintage electronics etc.
Day Job: Mostly LEDs
 
The following users thanked this post: Kean, Wolfram, Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #69 on: August 30, 2021, 02:18:58 pm »
Quote
Type B's start at around £100
Thanks, BTW, sorry  i forgot to add, that we dont need the type B RCD to contain the relay...just the signal.

Also, BTW, RCD in EVSE is covered by standard EN62955 (which we cant afford yet) .....as you know, its a "30mA/6mA" RCD,  and these can be made  "home-brew" style very cheaply (a lot less than £100).....what is the cheapest you think a  "home-brew" RCD (Type B)  could be done for? (for use in EVSE)...and not inclduing the relay...just the signal
« Last Edit: August 30, 2021, 03:59:14 pm by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19524
  • Country: gb
  • 0999
Re: Current sensing in an EV wall box
« Reply #70 on: August 31, 2021, 09:50:50 am »
Thanks, but those offtheshelf RCDs are upwards of 30 euros each.

With an EVSE, i am not sure if the standards require DC detection, or just an assurance that any DC fault current wont blind the RCD.?

I know the metrel EVSE testers actually do a test for DC leakage current, and if the EVSE doesnt trip at >6mA DC  than thats a fail, (or at least, a fail according to the metrel tester)....whether its a standards fail i dont know.?
For goodness sake. Don't be such a niggard. Spend the money. Failing to design this properly will result in greater costs, later on!
 
The following users thanked this post: Faringdon

Offline pardo-bsso

  • Regular Contributor
  • *
  • Posts: 201
  • Country: ar
Re: Current sensing in an EV wall box
« Reply #71 on: September 01, 2021, 02:06:57 pm »
Tangential to this,

I'm not sure if I understand the problem properly.
I assume (based on this thread and the others...) the current flows from mains, thru the charger and thru the car making a closed loop under normal conditions.

A fault to earth or unsuspecting engineer will divert some of it, no matter if it happens before or after the charger and that difference will be picked up by an rcd upstream.


At least here a simple test of that worked (and the quality of most of our breakers/protection devices is on par with Simons recollection of Italy)
 
The following users thanked this post: Faringdon

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2117
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: Current sensing in an EV wall box
« Reply #72 on: September 01, 2021, 03:02:20 pm »
Tangential to this,

I'm not sure if I understand the problem properly.
I assume (based on this thread and the others...) the current flows from mains, thru the charger and thru the car making a closed loop under normal conditions.

A fault to earth or unsuspecting engineer will divert some of it, no matter if it happens before or after the charger and that difference will be picked up by an rcd upstream.


At least here a simple test of that worked (and the quality of most of our breakers/protection devices is on par with Simons recollection of Italy)
Correct. But.... if there is a DC leakage current (EV battery charging electronics?) it can 'blind' a normal RCD (by magnetizing the CT).  The 'Type A' RCD must not be blinded by <6mA DC - technically any more than this can blind/desensitize a 'Type A'.
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 
The following users thanked this post: pardo-bsso, Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #73 on: September 01, 2021, 06:25:11 pm »
Thanks, is the DC leakage of 6mA (or more, eg 20mA DC)  actually dangerous, or is it just bad because it can blind the RCD?
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2117
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: Current sensing in an EV wall box
« Reply #74 on: September 01, 2021, 07:15:06 pm »
Thanks, is the DC leakage of 6mA (or more, eg 20mA DC)  actually dangerous, or is it just bad because it can blind the RCD?
IT'S THE FUCKING RULES!
Irrelevant - it's just what the standards say.
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 
The following users thanked this post: Faringdon

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19524
  • Country: gb
  • 0999
Re: Current sensing in an EV wall box
« Reply #75 on: September 01, 2021, 07:16:29 pm »
Thanks, is the DC leakage of 6mA (or more, eg 20mA DC)  actually dangerous, or is it just bad because it can blind the RCD?
DC is less likely to cause death, compared to the same mains frequency AC, but 6mA of leakage is still bad, whether it's AC, or DC.

An RCD being blinded is only dangerous, if there's a lethal leakage current to earth. It isn't dangerous, if there's no leakage. RCDs only became widespread over the last 30 years. Before that, proper insulation, earth connections and fuses/circuit breakers provided protection against electric shock. RCDs are only one layer of shock protection.
« Last Edit: September 02, 2021, 09:27:40 am by Zero999 »
 
The following users thanked this post: Faringdon

Offline pardo-bsso

  • Regular Contributor
  • *
  • Posts: 201
  • Country: ar
Re: Current sensing in an EV wall box
« Reply #76 on: September 01, 2021, 08:58:09 pm »
if there is a DC leakage current (EV battery charging electronics?) it can 'blind' a normal RCD (by magnetizing the CT).  The 'Type A' RCD must not be blinded by <6mA DC - technically any more than this can blind/desensitize a 'Type A'.

Thanks! I totally missed that aspect.
 
The following users thanked this post: Faringdon

Offline nightfire

  • Frequent Contributor
  • **
  • Posts: 585
  • Country: de
Re: Current sensing in an EV wall box
« Reply #77 on: September 01, 2021, 09:39:46 pm »
And for this reason a RDC type B is not allowed behind a RDC type A- because the type B would allow for far greater DC leakage currents than 6 mA and therefore provide false safety.
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #78 on: September 03, 2021, 08:38:08 am »
Thanks,
As you  know, if there's only one item of equipment being supplied, then it doesnt matter if you use Type A and/or Type B, in any order, as long as  a relay trips off the connections in the event of DC >6mA or AC imbalalance >30mA.
« Last Edit: September 09, 2021, 09:56:35 am by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline alexnoot

  • Contributor
  • Posts: 27
  • Country: aq
Re: Current sensing in an EV wall box
« Reply #79 on: September 03, 2021, 02:37:32 pm »
I think your 'product' will simply not be needed.
It will be badly designed, it won't adhere to any standards (as you can't afford them), and it will probably never work as you don't seem to know anything about what you're doing.

What is your actual job?
 
The following users thanked this post: pardo-bsso, RoGeorge, bdunham7, Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #80 on: September 03, 2021, 05:52:03 pm »
Thanks, Finance assistant at a startup in London

(this is for a sensor which will detect 30mA imbalance current in 32Arms wires...and also detect 6mA DC and more.
« Last Edit: September 09, 2021, 10:08:31 am by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 
The following users thanked this post: pardo-bsso

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 7992
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #81 on: September 03, 2021, 05:57:19 pm »
What is your actual job?

Stacking shelves at Tesco. Or it should be.
 
The following users thanked this post: pardo-bsso, alexnoot, Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #82 on: September 04, 2021, 11:36:11 am »
Quote
Stacking shelves at Tesco. Or it should be.

...Thanks, I am going to go into business making RCDs.
They are the most over-engineered and over expensive thing in the world!

« Last Edit: September 09, 2021, 10:07:02 am by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2117
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: Current sensing in an EV wall box
« Reply #83 on: September 04, 2021, 11:52:54 am »
Quote
Stacking shelves at Tesco. Or it should be.

...Thanks, I am going to go into business making RCDs.
They are the most over-engineered and over expensive thing in the world!

....all you have to do  is you get your mains live and neutral running through the torroid aperture.......then you simply shove a square wave voltage into the sense coil.......then the voltage that gets looked at, is simply the voltage across a low value resistor in series with the sense coil.....(its put in series with the coil "gnd" connection and ground)........and you then see either a symetrical waveform if no DC and no imbalance...or otherwise its non symetircal..........in fact, all you have to do is buffer it, filter it, then read it into an ADC....and its job done. Why is not everybody doing it like this?.....no feedback is needed.
No "square law" core is needed.
So why is nobody doing this?
Why is everyone paying >£30 for an offtheshelf RCD?

..the way described is inaccurate a bit, but you easily calibrate that out in production....just measure the coil core characteristics of the parts before building them up....

(this is for a sensor which will detect 30mA imbalance current in 32Arms wires...and also detect 6mA DC and more.)
Genuinely good luck for your venture.
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 
The following users thanked this post: Faringdon

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #84 on: September 04, 2021, 12:06:43 pm »
What is your actual job?

Stacking shelves at Tesco. Or it should be.

...Thanks, I am going to go into business making RCDs.
They are the most over-engineered and over expensive thing in the world!
...

I'm not sure what you mean by over-engineered, I'm greatly in favour of devices that can reliably detect leakage current and safely interrupt at least 6kA, and obviously rigorously tested to meet all relevant approvals.

You should also note that the IET wiring regs (which you have presumably purchased by now) stipulate that only breakers approved by a consumer unit manufacturer (basically meaning their own!) may be used in their enclosures. It's something of a closed-shop from that perspective - they will have no interest in approving your 'RCDs'. [Edit: In your case, Section 740 may have some relevance too.]


Personally I think Monkeh has done you a great disservice, I think you should set your sights on Waitrose!
« Last Edit: September 04, 2021, 12:33:11 pm by Gyro »
Best Regards, Chris
 
The following users thanked this post: Faringdon

Offline alexnoot

  • Contributor
  • Posts: 27
  • Country: aq
Re: Current sensing in an EV wall box
« Reply #85 on: September 04, 2021, 01:53:39 pm »
...Thanks, I am going to go into business making RCDs.
They are the most over-engineered and over expensive thing in the world!

So you've given up on your EV charger project then? Or is this just another thing?
You should design your own electric car too! They are probably over-engineered and overly expensive too, a lot of corners could be cut to make one on the cheap!
 
The following users thanked this post: RoGeorge, bdunham7, Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #86 on: September 04, 2021, 02:02:59 pm »
Quote
safely interrupt at least 6kA
We would just do a signal version...customer would need to put in their own contactor/relay.
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #87 on: September 04, 2021, 02:04:14 pm »
Stop it, you're killing me! :-DD
Best Regards, Chris
 
The following users thanked this post: alexnoot, Faringdon

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 7992
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #88 on: September 04, 2021, 02:07:56 pm »
Quote
safely interrupt at least 6kA
We would just do a signal version...customer would need to put in their own contactor/relay.

£30 RCDs are too expensive, let's make a £5 one to use with a £30 contactor!

Good grief, it hurts. Please stop.
 
The following users thanked this post: alexnoot, Faringdon

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2117
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: Current sensing in an EV wall box
« Reply #89 on: September 04, 2021, 02:44:01 pm »
Quote
safely interrupt at least 6kA
We would just do a signal version...customer would need to put in their own contactor/relay.
I didn't see that coming. I guess time will tell if 'the people' want your idea.  I'd probably do some market research before committing funds to this endeavour.
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 
The following users thanked this post: Faringdon

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 7992
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #90 on: September 04, 2021, 02:56:13 pm »
Oh, and in this genius plan of yours, have you calculated the operating costs of the contactor coils?

Your imaginary savings are just that.
 
The following users thanked this post: Faringdon

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #91 on: September 04, 2021, 04:58:43 pm »
You probably also want to look at pictures of the internals of an RCD - contact opening speed, spacing of open contacts, arc cooling plates, arc chute etc. and compare with a typical contactor - there's no comparison. I don't know where you could source a contactor / relay style device that would have similar construction - at any realistic price anyway.

You probably have a signal level driver with absolutely nothing suitable to drive!  You definitely need to start researching this stuff before you come out with it.
Best Regards, Chris
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #92 on: September 04, 2021, 05:25:56 pm »
Quote
£30 RCDs are too expensive, let's make a £5 one to use with a £30 contactor!
Thanks, but sorry if i misled.........if you buy an RCD that contains a contactor, then its a minimum of £100 that you'll be shelling out.!.....

Type B RCD with contactor...£100...cheapest out there!!!
https://shop.evchargersdirect.co.uk/products/type-b-rcd-rccb-40a-for-ev-charge-point-installations-2-pole-single-phase-30ma-ekl1-63?variant=31988378140768&currency=GBP&utm_medium=product_sync&utm_source=google&utm_content=sag_organic&utm_campaign=sag_organic&gclid=EAIaIQobChMI3LzRxenl8gIVrWYVCB2f5wIQEAEYASABEgIRT_D_BwE

Soon we will take this market!

Quote
You probably also want to look at pictures of the internals of an RCD - contact opening speed, spacing of open contacts, arc cooling plates, arc chute etc. and compare with a typical contactor - there's no comparison. I don't know where you could source a contactor / relay style device that would have similar construction - at any realistic price anyway.
...we would source from our Chinese contacts....just like everyone else already does....including the so-called "standards compliant" ones.

Quote
Stop it, you're killing me!
Thanks, we will indeed make some that contain both signal circuit and contactor.
« Last Edit: September 04, 2021, 05:31:34 pm by Faringdon »
'Perfection' is the enemy of 'perfectly satisfactory'
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 7992
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #93 on: September 04, 2021, 05:29:49 pm »
Quote
£30 RCDs are too expensive, let's make a £5 one to use with a £30 contactor!
Thanks, but sorry if i misled.........if you buy an RCD that contains a contactor, then its a minimum of £100 that you'll be shelling out.!.....

Type B RCD with contactor...£100...cheapest out there!!!
https://shop.evchargersdirect.co.uk/products/type-b-rcd-rccb-40a-for-ev-charge-point-installations-2-pole-single-phase-30ma-ekl1-63?variant=31988378140768&currency=GBP&utm_medium=product_sync&utm_source=google&utm_content=sag_organic&utm_campaign=sag_organic&gclid=EAIaIQobChMI3LzRxenl8gIVrWYVCB2f5wIQEAEYASABEgIRT_D_BwE

Soon we will take this market!

That has nothing to do with 'containing a contactor' and everything to do with 'type B RCD with low volumes'.

You're not taking any market. If you do somehow get to market there's no way I'd ever trust a product you've had a hand in anywhere on my property.
 
The following users thanked this post: Faringdon

Offline FaringdonTopic starter

  • Super Contributor
  • ***
  • Posts: 1995
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #94 on: September 04, 2021, 05:33:34 pm »
Quote
That has nothing to do with 'containing a contactor' and everything to do with 'type B RCD with low volumes'.
Thanks, but you cant really buy them much cheaper even if your volumes are high.....and to be honest, if you have high volumes...the lead times theyll give you are so ridiculously long
'Perfection' is the enemy of 'perfectly satisfactory'
 

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9506
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #95 on: September 04, 2021, 05:41:31 pm »

Quote
You probably also want to look at pictures of the internals of an RCD - contact opening speed, spacing of open contacts, arc cooling plates, arc chute etc. and compare with a typical contactor - there's no comparison. I don't know where you could source a contactor / relay style device that would have similar construction - at any realistic price anyway.
...we would source from our Chinese contacts....just like everyone else already does....including the so-called "standards compliant" ones.

 :palm:  These are presumably the same Chinese contacts (Customer?) that you haven't yet told that you have no clue what you are doing, and who are currently spending their money setting up multiple production lines!

There is no 'so called' when it comes to safety standards! Not unless you personally import fake shit anyway!
Best Regards, Chris
 
The following users thanked this post: Faringdon

Offline dmills

  • Super Contributor
  • ***
  • Posts: 2093
  • Country: gb
Re: Current sensing in an EV wall box
« Reply #96 on: September 06, 2021, 12:51:47 pm »
There actually ARE 'earth leakage relays' that control external contactors, but you will not find them in domestic or even small scale three phase installs, these go to the industrial panel builders and are typically used together with zero phase current transformers and some seriously butch shunt trip switchgear. Remember an RCD is NOT AN OVERLOAD device, it does NOT have to break the PSC, so it has a substantially easier switching role then an RCBO or MCB has.

Nobody playing in this space gives a shit about a hundred quid for a safety component, in fact I get increasingly twitchy as the price of such things falls.
Also, nearly nobody pays list price for this gear, you generally get at least 20% off down the wholesalers for knowing enough to ask for it.

 
The following users thanked this post: Faringdon