Hi,
let me start with a short description of the current state:
I have (mostly) 2 machines with a big motor with their typical start current spike. One 2.2kW air compressor and a ~1kw water chiller, both single phase. Both can't be equipped with a soft start.
Incoming supply from grid: 3 phase 230/400V (Germany), seems like very high wire resistance or so.
Rental garage place, no touching of electrical before the single 3-phase outlet.
Issue: After the rental company did "changes", the starting current brings down the voltage to an unacceptable level, even across other phases. The light (no touchy zone) goes almost out,
even running on a different phase.
And running both heavy loads at the same time, I'm afraid of damages, even across phases.
So my question is:
Is there a battery unit (similar to a UPS) that can bridge the power demand for a few seconds in addition to the power from the grid. Something where I can set to ~220V instead of the normal ~240V
so it only triggers and pumps power when the power spike happens. I don't want to back feed into the grid. Manually turned on only when I need the compressor.
I can't measure the start power, but assuming it's the normal ~6-8x range, we are speaking about 17kW - 3-4kW or so from the grid. Enough to trigger a 10A class B circuit breaker, class C is fine.
I need that only for a few seconds until the grid can handle it again (barely, you can see the light flicker on the peak of the compression).
I don't need high capacity, just a short power delivery. 1kWh capacity would be plenty, but the ~17kW peak might be an issue.
Any suggestions for devices that don't cost an arm or leg?
Moving is not an option, looking for a replacement place for years
Cheers Grumpy