Author Topic: Grid Tie Inverter w/Limiter and "Back Feed"  (Read 4068 times)
Offline OpenCircuitTopic starter
« on: December 21, 2024, 02:03:00 am »
How does this* grid tie inverter (2000w DC50-90V) monitor both phases independently in the US with split phase and only one clamp? Is it even possible to not "back feed" into the grid with this setup? Page 1 of the pdf has both methods and the images. One person claims he was able to get it working with two clamps in series, but I don't know how this does not end up with a back feed on at least one phase under ideal conditions. I can't quite comprehend the translation. Thanks for any help.
*Link: https://www.amazon.com/dp/B08F9Y6WKJ?ref=ppx_yo2ov_dt_b_fed_asin_title&th=1
« Last Edit: December 21, 2024, 02:12:06 am by OpenCircuit »
Offline Someone
    • send complaints here
Re: Grid Tie Inverter w/Limiter and "Back Feed"
« Reply #1 on: December 21, 2024, 04:28:13 am »
The explanation is fairly explicit, those configurations are for using the inverter to power 240V (line to line) loads only. You put the current clamp in a spur running to the line to line loads.
The following users thanked this post: OpenCircuit
« Reply #2 on: December 21, 2024, 05:19:53 am »
OK, so the phase not being monitored just matches the monitored phase.
Offline David Hess
  • DavidH
« Reply #3 on: December 21, 2024, 08:51:06 am »
It does because it is only monitoring 240 VAC loads which are connected between the phases.