Sounds great! I didn't know Enphase has wireless power modules these days...
All things considered I'm not sure what qualifies as safer. Either way you need cabling on the roof. The mains grid has an awfull lot of power behind it. Sure current can be limited by fuses but still it can push 3kW+ into something to cause a fire. Not to mention a large current surge ability. A string of solar panels can push a lot less power.
You may not be familiar with the system, but what he is getting at is that there are no splices, combiner boxes or any other wiring assembly done on the roof. The cabling comes preassembled, you plug in the modules and the other end goes back through a feed-through so that all of the splicing and connection is done inside.
As for 'what qualifies as safer', instead of speculating whether a 240VAC (think about the AC part) limited by a 20A breaker is less of a fire hazard than 800VDC limited to ~8-10A typical with no off switch, we can just look at the incident rate for installed systems over the past decade or so. I think there are three reasonable conclusions:
1) Most if not all of the fires have been in HVDC systems. That includes all the burnt Wal-Marts as well as small burnt-up things like Dave Jones' isolator box.
2) The overall reliability rate of each type is not readily ascertainable, at least not to me. Neither is perfect. Enphase had a whole batch of unreliable inverters early on and apparently you've seen some issues with the contactor-thingies. OTOH, when I installed my system installers were routinely replacing the HVDC inverters which failed fairly often. Most systems that I see or hear of nowadays that aren't working are plain string systems, but that's a small, localized sample.
3) Either type of system works pretty well if you manage to avoid the defective components and the installer does a good job.