f4eru:
Seems like an LC network, i.e defined impedance that is connected between neutral and PE ?
then it triggers an RCD if the neutral deviates from PE.
Works only of course if the defect is after the bonding point, or if the PE comes from a separate earth rod...

Could it be that the LC is tuned to 50Hz, so that normal sine does not pass, but HF/harmonics of DC will trigger the RCD ?
I would have expected more like a 25V VDR or so.


In any case, it's probably not nice, because injecting currents into the RCD can make it inefficient against it's original purpose....
excrucio:

--- Quote from: f4eru on Yesterday at 07:16:40 pm ---injecting currents into the RCD can make it inefficient against it's original purpose....

--- End quote ---
there is no current until it is N fault, and when it is it is not big. so rcd works as it is intended