MindBender:
Hi,
I recently bought a 240V/120V step-down transformer to power my 120V JBC soldering tools from our 240V mains. It’s ha hefty 2000VA version, because both tools are 700Watt each, and 1500VA seemed a bit tight.
Now when I switch it on, even if it has no load connected to it, the circuit breaker for that circuit trips. It is an ABB, 16A B-profile with internal 30mA GFCI.
At first I thought it was tripping because of a ground fault, but disconnecting PE didn’t make a difference. However, connecting it to my isolating transformer did make a difference; The circuit breaker didn’t trip, but at switch-on the isolating transformer made a clean 50Hz hum that faded out in a few seconds, so it may be high inrush current, and a rather long one at that.
When I used my variac for the same purpose before I bought this step-down transformer, the circuit breaker also tripped every now and then. Both step-down transformer and variac are mono-transformers, transformers with just a single coil.
Does anybody know what’s going on here? And how I can fix this, if it is fixable?
Thanks in advance.
MF-jockey:
The high inrush current is caused by the magnetization of the transformer.
https://youtu.be/kn9QOF5d-Sw
When I switch on a larger transformer, I use a series resistor (wire resistor 15 to 68 ohms, at least 10 W type) and a time relay which bridges the resistor after about a second.
The resistor should be mounted in such a way that it cannot cause a fire if the relay fails.
There is also a circuit variant with NTC and relay.
Then there is the luxury variant, the electronic transformer switching relay "TSRL" from FSM AG.
https://www.fsm.ag/de/trafosanfteinschalter/produkte/tsrl, sorry only in german.
MindBender:
--- Quote from: MF-jockey on September 05, 2023, 10:46:02 pm ---The high inrush current is caused by the magnetization of the transformer.
https://youtu.be/kn9QOF5d-Sw
--- End quote ---
Thanks for your reply!
The good news I take from this is that it is a very normal and well-understood phenomenon. Not well-understood by me though; The inrush seems to last longer than 1/4 for the wave period. I've watched the video, and I'm sure people with a better understanding of the integral formulae shown will understand why. But I'm not pursuing that understanding right now.
--- Quote from: MF-jockey on September 05, 2023, 10:46:02 pm ---When I switch on a larger transformer, I use a series resistor (wire resistor 15 to 68 ohms, at least 10 W type) and a time relay which bridges the resistor after about a second.
The resistor should be mounted in such a way that it cannot cause a fire if the relay fails.
There is also a circuit variant with NTC and relay.
Then there is the luxury variant, the electronic transformer switching relay "TSRL" from FSM AG.
https://www.fsm.ag/de/trafosanfteinschalter/produkte/tsrl, sorry only in german.
--- End quote ---
Interesting! This TSRL comes in many variants, of which the simplest is exactly what you described; An NTC with a timer relay to bridge it:
http://www.trafo24.com/epages/79921744.sf/de_DE/?ObjectPath=/Shops/79921744/Products/TSR-0016
Unless you have all parts laying around (which I probably have) and you still know where to find them (which I probably do not), the price is pretty hard to beat for something pre-made, tested and working.
There's also a version that prevents the inrush current all together, instead of limiting it:
http://www.trafo24.com/epages/79921744.sf/de_DE/?ObjectPath=/Shops/79921744/Products/TSR-0009
I wonder if this is better for my application. It doesn't limit anything in case of over-current, the datasheet says, but NTCs have a limited life span. Decision paralysis...
Psi:
Could put a incandescent lamp in series with in the primary then a relay across the lamp with the relay powered off the output of the transformer. Not the best solution, but its easy to build with parts lying around.
woodchips:
Why not just change the MCB from the B rating to a D rating? D is for transformers, C for motors, B for lighting, A for resistive, just the amount of inrush current the load has.