All batteries read 12V or above alone and the total of all 8 on the battery cartridge is 54V at the cartridge terminal right?:Yes this is correct, on average they read about 13.3v.
Under load the battery cartridge drops to 50V with less than 40% and close to 46V above 40%, giving the overload error, right?Yes, the entire cartridge drops to 50v rapidly when load us under the overload threshold, and 46V when above the overload threshold.
A new cartridge by APC standards should be 48V with a nominal capacity of 10Ah, for your info. A bank of 4x 12V batteries in series (48V) in parallel with a second bank.It does seem like mine follows the APC standards then.
The smell you feel after the UPS is turned off is like a kind of alkaline smell who looks like you can smell with your mouth (I know it's strange what I've written, but is what the smell I think it is looks to me when I feel it)?I'm not entirely sure, but it's certainly not like anything I've smelt before.
The inbuilt self-test of the UPS says everything is OK with the battery cartridge right (Press and hold the I/Test button for a few seconds to initiate the self-test.)?Yeah it does pass according to the management interface.
I noticed that the logs of the UPS show that the %VAOut and Iout spikes during these overload sessions. Amps spike to about 18A out from the
normal 0.00A, and %VAout spikes to to about 35% to 70%.
Actually looking at the logs normally it always report 0.0A out and 0% watt out under normal load, I wonder if this is an issue or if the UPS is just reporting output amps while on battery...
Below you will find a spreadsheet of the last test I have done. Note that the starting capacity was low as it took a few tries for me to get it to show both a working self test and two overloads, one of which reporting a low battery condition. This was tested with a small load of about 345W.

Here is an overload I tester earlier, notice how the battery quickly drops to 64% capacity.
I had a similar problem but with a smaller SUA1500RM2U with 2 banks of 2 batteries each and it was a battery who would drop is voltage to low 9V immediately when provided work on her.I'm not knowledgeable on batteries, but it could be that they aren't good. The high amp output by the UPS when on battery is a bit worrying though...
Thanks for taking your time to read over this for me, I do appreciate that.
With the price of batteries coupled with the fact that I'm not confident it's the batteries, I don't really want to have to buy 8 more just to test them.
(Seems battery stores don't like you returning batteries after you've left the store unless they are actually faulty, so if it's the device and not the batteries I would be stuck with an extra 8 batteries.).
What I might do is purchase another unit... That way I may actually have a working unit that I can test the new unit batteries on the old unit. Seems to kill two birds with one stone, well a diamond in this case given the $$$.