4 meter is a little short for a 200MHz scope. The fault could be hidden in the rising edge.
I have a couple techniques, depending on the situation, when the TDR route is impractical.
My most favorite gadget is a Carlson Superprobe (diy project from youtube). Instead of using a piece of coax as the probe, I added an SMA connector so I can change from an E-field probe (for open circuits) to an H-field probe (for short circuits). Audio is a bit tricky getting any distance with, but if you AM modulate a LF carrier, you can easily reach through a wall. Just don't go too high in frequency or it can couple to other conductors.
Another one of my tricks for really getting through walls, and this is primarily for following good cables, not necessarily for finding breaks, is to inject an HF carrier at the farthest outlet between the ground and neutral using a simple crystal oscillator and decoupling cap connected to an extension cord end and plugged in, and using a handheld radio scanner as a receiver with an H-field probe in place of the antenna. In this case, since the detection is with the H-field, current flow is required. Being the ground and neutral are connected in the box, that requirement is met. Assuming your break is in the hot wire, this may still work in your case for following the path of the wire.
Edit: I mention the latter HF + H-field trick because knowing where the cable is in the wall greatly aids in finding the weak e-field signals on the broken wire. As has been said, getting a tone from a few inches away is sometimes tricky, but knowing right where to look may help you pick up the signal after losing it in a corner or something.
Edit2: and don't be afraid of trying to get a tone on the outside of the wall. In some pre-fab or lazy builds, instead of drilling a hold in the stud, a notch is cut into the face of it and covered with a metal plate. Often times, these are on the outside face of the wall,so getting a tone on the inside may be hard.