Got the following: (500W AC Voltage Regulator Variac Variable Auto Transformer 110V Metered 130V) from Ebay and found the following errors:
Neutral (brown wire) incoming wired through on/off switch and fuse, connected to 120 volt transformer input but wired to neutral outlet terminal.
Hot (blue wire) incoming wire directly to transformer common input.
Transformer variable output wired to hot outlet terminal.
Besides the obvious hazard of all output terminals becoming hot when switched off or fuse blown, voltage between ground and neutral outlet terminals will vary depending on transformer setting and load.
Be aware of and correct these problems if using this transformer to power your instrument for testing purposes.