Hi,
I have a Borri B8033 UPS rated at 40kVA. The UPS is working, but the output filter inductor of one phase is buzzing rather loudly, it probably is indicating some kind of problem. The noise is lower when the load is higher.
My LCR meter shows higher inductance for that inductor, compared to the other two phases (it also shows lower Q at 10kHz).
The driver module for the output IGBT shows signs of getting hot (electrolytic capacitors were kinda bad, the board itself is slightly discolored), but I have no idea which came first - something happened to the driver board and that messed up the inductor or the driver board is getting hotter because of the inductor (or it may be not related). The output filter capacitors are OK.
The buzzing inductor measures:
f,Hz L,uH Q ESR
100 860 6 0
1k 790 12.5 0.39
10k 706 7.69 6.76
100k 510 2.54 126
Another inductor measures:
f,Hz L,uH Q ESR
100 730 5.8 0
1k 680 11.67 0.33
10k 615 9.05 4.25
100k 470 2.83 103.8
The third inductor measures:
f,Hz L,uH Q ESR
100 737 5.79 0
1k 662 13.2 0.33
10k 600 8.7 4.26
100k 451 2.75 103
So, the buzzing inductor has much higher inductance than the others. It looks exactly the same, so I think that there is some kind of fault.
What kind of fault could cause the inductor to buzz and to measure higher inductance value?