Hi group, this is a new one for me, and I'm posting to see what youall think about it. Safe? Concerning? A design flaw?
I was recently working on battery troubleshooting a 5SC series UPS - 5SC750. While taking some signals measurements I was shocked to find that the battery was AT LIVE LINE LEVELS while the system was in normal operation.
Typically one assumes that the battery in UPSs that don’t have live voltage warning labels are at most at their own potential with respect to ground - 24 - 48V and of course can source a lot of current to be cautious of. However in the 5SC750G system, a 230 V UPS, the battery terminal voltage drops to over -320V with respect to ground, and can sink AMPS of current! This seems to be a serious risk.
Just a word of caution to those out there who may be working on them, be careful! There is no sticker warning around the battery that it is reaching negative line voltages, battery cases aren’t typically designed/rated to withstand hundreds of Volts, and the surge potential isn’t just from the battery voltage but from line power.
Because the battery is housed in a grounded case, this means the walls of the battery are withstanding cyclic -340V of potential in the 240V model of UPS.
This also means that if a user is doing tests and connects the battery while it is sitting outside the unit, they could be electrocuted if they touch the battery terminals and ground (the case). To me, this is just nuts, but what do you think? If there's interest I could post scope plots, etc.