Author Topic: Help running this 220v machine in my house  (Read 5805 times)
Online themadhippy
Re: Help running this 220v machine in my house
« Reply #50 on: February 22, 2023, 09:32:19 pm »
As long as nothing is relying on the mains frequency for timing
Offline james_s
« Reply #51 on: February 22, 2023, 09:35:40 pm »
There's no timer, it's nothing more than a heating element with a bimetal thermostat.
Online themadhippy
« Reply #52 on: February 22, 2023, 09:43:06 pm »
i was replying to the 2  posts directly above mine
Offline administr4torTopic starter
« Reply #53 on: February 22, 2023, 09:45:26 pm »
dangerous Chinese appliances, bad record of fire, poor wiring unsafe insulation
I would not use  such junk in my house.
Check out the approval of the Chinese appliances, the safety compliance trademark may be counterfeit
Thus no valid UL, ETL, CE safety test.
Incase of any incident you will be responsible and liable
Be safe!
j
thankssomuch for warning.
these are things i am doing
- I am using this machine only in 14-50P nema plug rated for cooking oven 50Amps
- I am not using it continously for hours and hours, since its steam cleaner, I have to start and stop it many times
- the machine is always in my view
- i have fire extinguisher in my reach 24x7
can someone please tell me if 14awg wire is good enough to extend this machine cord?
factory cord is short for my usage from NEMA plug
« Last Edit: February 22, 2023, 09:49:00 pm by administr4tor »
Offline james_s
« Reply #54 on: February 22, 2023, 09:55:26 pm »
I wouldn't hesitate to use it. Actually I'm tempted to buy one myself for cleaning stuff underneath cars.
#14 wire is good for 15 amps, if this thing is 3kW it will draw 12.5A so you should be fine. Depending on the length you might want to go with #12 wire, it's not *that* much more expensive. I like SJOOW or SOOW for this type of thing.
Offline shapirus
  • Country: ua
« Reply #55 on: February 22, 2023, 10:27:16 pm »
Yeah that's obvious. The only thing that comes to my mind are magnetic transformers, but as far as I understand the theory correctly, those designed for 50Hz will generally be happy to work at 60Hz. It's the opposite that would not necessarily be true.
Offline james_s
« Reply #56 on: February 22, 2023, 10:34:51 pm »
Yes, any 50Hz transformer ought to be fine on 60Hz, it will run cooler and be more efficient, same with motors and solenoids. The opposite may not be true, if there is just enough iron for 60Hz it will saturate at the lower frequency.
« Reply #57 on: February 22, 2023, 10:46:53 pm »
James i need 30-40 feet of length extended. do you think 14awg will work?
Offline shapirus
  • Country: ua
« Reply #58 on: February 22, 2023, 11:01:16 pm »
Power lost as heat in this extension cord will be about 30W at 12.5A or 30W/(40ft*2) = ~0.4 W/ft, or double that if you calculate this for the 2-wire units of length. This isn't going to heat it up to a noticeable level, unless it's kept in a roll, and the voltage drop is going to be about 1%, so it should be ok.
« Last Edit: February 22, 2023, 11:02:58 pm by shapirus »