For proving a high energy electrical circuit a general purpose multimeter is not really the preferred equipment, and being safe doesn't need to be expensive in equipment cost, just as a basic example, A Fluke T90 can be had for as little as 50 quid new.
In the industrial setting I would say that technicians not proving disconnections and not putting shorting links on remote high energy circuits are the biggest source of accidents, perhaps only behind circuit identification mistakes, and multiple source "gotchas".
PV and their inverters are good traps for the unwary...
As for using cheap multimeters, I'm not knocking them, they're great value things, and safe when used within their ratings and with common sense.
My routine for working on any part of a fixed electrical installation is:
Prove the testing device.
Identify the circuit.
Switch off the breaker, and lock it off, plus tag the circuit as isolated.
Prove the circuit is dead.
Prove the testing device.
If you do not have control over the operation of the breaker then fit a suitable shorting link on the circuit.
X