This 90VAC could be the difference between mains earth and mains neutral. This can occur when the mains voltage "floats". Can be caused by many thins such as poor load balancing on the 3 phase line supplying your area.
This is easy to verify with a DMM. But for ungrounded switchers, I think it's more likely that it's due to a capacitive voltage divider formed by the input filter caps.
I have this problem at home with a poor earth connection. The voltage between neutral of my cellphone charger and my body for example gets up to around 80VAC when the weather has been dry for a few weeks. It can give a stinging tingle if you make contact with it.
Cell phone chargers (which are usually double isolated, so nothing to do with ground potential) should not allow any significant current to flow between people touching it and either the live or neutral. Both are considered identical from safety perspective in consumer equipment.
The mains neutral and mains earth should be at the same potential and solidly connected to the ground by way of a ground spike. They should be connected together on the supply side of your home distribution board. Connecting earth to neutral on the load side of your home distribution board can lead to your RCD (residual current detection) circuit breaker tripping all the time.
This depends on the local earthing system (eg. TN-C vs. TT). Some systems may even have ground in the middle between the two other conductors (eg. on ships). Connecting any other conductor to ground could cause some serious fireworks in that case. Even in TN-C systems, neutral and ground are usually not at the same potential, since the neutral wire carries current, and the ground wire doesn't, so the neutral wire has an IR drop (this is actually a neat way to measure wiring resistance). Allowing ground to carry current defeats the point, you'll just have to parallel neutral wires, and no additional safety compared to WO2-era appliances (chassis connected to neutral).
In my opinion, it's a bad idea to tell people to mess with safety features of electrical wiring, unless they know what they're doing, but in that case they wouldn't need anyone to tell them what to do. Especially if you don't know someones location, electrical system or regulations.