As Zero999 says, heat dissipation of an SSR will be significant. Go for something like the Finder 65 series mechanical relay, 30A rated with double break contacts. It is smaller, more efficient and way cheaper than the equivalent SSR.
Good point, thanks! One thing about the Finder 65's specifically (65.31, 65.61), Digikey is listing them as obsolete and unavailable while element14 gives no indication of problems, is that just a glitch with Digikey?
And a general question about SSR heat dissipation, just for my own education, the data sheets for the Panasonic SSRs I looked at as examples had fairly modest heatsinks even for 30-40A loads and had curves at 10A for no-heatsink use, do they really dissipate that much heat?
I don't know. RS in the UK have stock of some coil voltages, others are back order (June). Farnell (element 14), UK of course, have most voltages in stock. Presumably you only need one, maybe a spare. I don't know what coil voltage you're looking for.
Regarding SSR dissipation. Zero999 did the sums (reply #37), they look correct to me. Heatsinking requirements depend entirely on thermal resistance to ambient, ambient temperature, and maximum permissible /
desirable operating temperature. In the UK, hot water tanks live in the airing cupboard (for airing -not drying- laundry). Inside temperature is significantly above the rest of the house. I don't know your situation there.
The AC1 rating of that particular relay is 7500VA. De-rating by ~50% for a heater load is my sweet spot for a long and happy life. I probably wouldn't be tempted to go for a lower contact current. The cost saving doesn't really make it worthwhile and you typically lose the desirable 3mm contact separation.
Edit: As I indicated in Reply#38, the total power loss of the finder relay is 3.1W at full 30A contact load. Given that the coil contributes 1W, running the contacts at <15A probably takes the total dissipation to <2W. Omron used to do a similar spec relay in the same for factor, I don't know if they still do.