It looks like many failures, just in the substation alone.
I worked in the utility industry SCADA and transformers have many sensors. Sudden pressure sensor (SPR), Buchholz relay, pressure relief valve switch contact etc.
There are other sensors, typically: oil temperature 26T, winding temperature 49T, low oil level main tank 71T and conservator 71A, cooling fan fail etc.
There can also be a differential protection relay 87T which monitors current (power) in and out. If an internal arc occurs there is a big difference which means trouble, they trip in 30msec.
The protection relays are supposed to trip breakers and disconnect power fast to prevent such a big fire in the first place.
You can see in Hayes pics there is also the fire suppression system that missed the boat. Red piping and sprayers surrounding each transformer.
These systems can get old and rarely tested.
The oil is typically mineral oil but less flammable silicon-based synthetics are used.