RCD's when they trip are performing out an important function in helping minimize the risk of electrocution and fire but can some times be seen as a nuance if the fault is intermittent and you have one RCD on the supply to all circuits in a distribution panel. So when it trips you loose everything and you are left in the dark.
Very commonly appliances that heat water (immersion heaters, kettles, steam irons, washing machines, hobs ect...) are the first to suspected often being that moisture is getting in the electrics or elements breaking down.
Followed by exterior power circuits (lights, power sockets ect...) are vulnerable to moisture ingress
Other types of heating appliances (ovens, grills, storage heaters ect...)
Pet or rodent damage to wiring.
Appliance cords getting trapped / snagged.
Faulty fixed wiring
Other faulty equipment.
There is also the possibility that RCD has a fault. There is test equipment for this and an RCD ramp test can be particularly useful in detecting over sensitive RDC's
In the UK it is now a minimum requirement for new installations that a split load distribution panel is fitted where by there are two 30mA 0ms RCD's in the panel so the properties circuits can be split across the two. Idea being when an RCD trips your not left completely in the dark.
The next stage on from a split load panel is to use RCBO's for each individual circuit. There is a higher installation cost (costs of RCBO's are dropping) but has the advantage of only the circuit with the fault present on it trips out. This helps with finding the source as you only have one circuit to check and all the other unaffected circuits carry on as normal.
In some circumstances there is another benefit to having individual RCBO's.
With the move away from using liner PSU's in devices to switching PSU's with some they can present a higher leakage current. (and also just having too much junk about the place needlessly left plugged in and switched on all the time)
So when you start totting up the actual leakage currents of all the devices connected it is possible to start knocking on the door of for instance the tripping point of a 30mA RCD, if there is just one covering the whole installation. Which can be a real pain when you are running about the place in the dark trying to work out what set the RCD off and not finding any faulty equipment or wiring.
But in any case if an RCD trips it should always be assumed that there is a fault that has to be found and isolated / fixed.