The claimed COP turns to ***t in conditions where evaporator icing is possible, which is basically anytime the humidity is above about 50%, which is most of the time The pump then has to go into reverse cycle to thaw it, which is ridiculous.
This is weird, because just today we have witnessed some very British weather: the whole day has been +1degC and RH exactly 100% + thick fog.
Number of defrost cycles between 7am and 7pm (right now) is:
2. For example, the previous run cycle:
Started at 15:32
Defrosted at 17:06
Finished defrosting at 17:11
Running at minimum power, reached upper temperature setpoint at 18:01 and stopped
There is nothing "ridiculous" in defrosting. It's completely normal, it's a feature, not a bug. Did you actually
measure or otherwise verify it's causing a problem? Or do you just "feel" it is "ridiculous"?
During the last 24 hours, 19.136kWh has been consumed by the heatpump. The heat as required by the house, to maintain +22degC indoors, at this weather, is approximately 50kWh/24hrs based on earlier calculations and tests. Additionally, the heatpump pre-heats domestic hot water, amount of which is hard to exactly say, but we have a 1.5 year old poo generator who needs butt washing and stuff like that, so with two showers, some dishwashing etc. I would quickly guesstimate at least 10kWh worth of hot water preheating took place. Therefore, COP would be around 60kWh/19.1kWh = 3.14.
Manufacturer test reports, which honestly says it ignores defrosting, and thus probably also ignores the bottom tray heater, and which also ignores water pump, which I do include in my numbers, states COP = 3.95 in similar conditions. Once you add water pump, it's down to 3.55. Once you add bottom tray heater, it's down to 3.09, nearly exact match with my estimate. This means the heatpump is doing excellent job with defrosts ending up with the same COP than in dry tests (which is unsurprising, if you read my previous longer post about it); and one could improve the heatpump, not by magically removing need for defrosting by dehumidifying the whole planet, nor by improving defrosting decision algorithms,
but by more intelligently controlling the bottom tray heater, which is something I haven't done yet; I have not modified the thing at all.
Does your system work, and have you measured the consumption to verify there is a problem? Or is this again some feeling mumbo jumbo?
here in the UK you can forget it if you want to achieve +21C inside with -8C outside, with radiators.
Also this is obvious bullshit, there is nothing special in UK climate at -8C compared to e.g. Finnish climate at -8C, RH varies between 85-100% anyway at that point. -8C and +21C is completely normal everyday operating point for me, and yes, with radiators, albeit admittedly swapped for larger sizes than original.