What are the implications to devices?
And BTW, can this happen with isolated transformers?
vk6zgo: Never mind me, I can take it. I just wonder what are some possible side effects to grounded devices that are connected, during normal and fault conditions.
I mistakenly assumed this was an isolation transformer because it's a laminated core type, but it does indeed seem to be an autotransformer. But can't you get similar results from an isolation transformer, line/neutral at 110V/220V above earth, depending on what output taps you use?
Richard: It's just a laminated transformer in a box, with a switch and a fuse. It was a bit surprising to see non-0V there because it's constructed cleanly enough.
There was a previous discussion here where it was revealed that in Nordic countries (at least, if not elsewhere), they treat BOTH sides as "hot", and only the green-wire safety ground can be relied on to be zero volts.
I wonder why plugging this in did not trip your circuit breaker?
I'm not entirely sure you understand how a circuit breaker operates.
I'm not entirely sure you understand how a circuit breaker operates.
It should trip if its a GFCI, should it not?
The 2 prong Europlug can be plugged in both ways, but the outlet itself still has an official line/neutral sidedness.
The 2 prong Europlug can be plugged in both ways, but the outlet itself still has an official line/neutral sidedness.
These days the only thing polarization really matters for is Edison light sockets where the neutral conductor is exposed. Most other devices are required to be isolated and/or grounded, so there should be no more danger of coming into contact with neutral than hot. They do at least keep live and neutral identified for fixed wiring, so at least permanently wired lighting fixtures should be connected with the correct polarity.
I'm not entirely sure you understand how a circuit breaker operates.
It should trip if its a GFCI, should it not?
Why would it?