Hi all,
For my first electronics project I've built a simple linear power supply to provide 70V to run steppers on a CNC machine I'm building. The circuit I've built is this:

The transformer is a 1000VA with 230V primary and twin 24V secondary in series. The bridge is a 35A, 400V part. Smoothing is provided by 40,000uF for electrolytic capacitors.
The problem I'm having is with the fuse. I started off with an 8A cartridge fuse but it blew about 50% of the time on start up so I switch over to a 6A Type D breaker. The breaker stays in most of the time but I get the occasional nuisance trip. From what I've read I think the problem is inrush current while the magnetic fields establish in the coil. If I understand it correctly the current can be huge if the AC voltage is near 0V.
Someone has suggested using slow blow or time delay fuses (I believe this
http://uk.rs-online.com/web/p/cartridge-fuses/5371313/ would be an appropriate part) but looking at the spec I can't see how that would be any better as it lets go under 50A surges. I'm guessing the coil must be pulling 100A+ on start up under the worst case conditions.
So I did a bit of searching and I came across this page
http://www.ametherm.com/inrush-current/transformer-inrush-current.html which discusses putting an NTC thermistor in series with the power supply for the coil like this:

Is this an appropriate part?
http://uk.rs-online.com/web/p/thermistors/2118002/I'm not too worried about wasting
a little power but I'd rather not dump loads of heat into my power supply case if I can avoid it. Using that 10 ohm part as an example though it looks like it has the potential to dump a lot of heat. Assuming it self heats to 85degC then the resistance drops to 1.5 ohms giving a 6.45V drop in the supply. At the maximum current for the coil of 4.3A that equates to 27W of heat! In reality the coil will never draw 4.3A as I've over spec'ed it but I'd like to make sure it's safe if it does.
I'm open to suggestions for other solutions too :-), cheers.