Exhibit 248
Beaver creek Ohio Fire(March7.2018):
"For example, Walmart understands that improperly sealed housing during installation permitted water intrusion into the Fronius inverter, which likely contributed to the fire's ignition.
Moreover, brass/metal bolts were used in the inverter fusebox(rather than fuses as required by both the Fronius manual and the National Electric Code)"
Bolts for fuses!
WTF!?!
Also blames the same inverter in another case and piss poor install maintenance on a third site.
Same exhibit
At Yuba City, CA, Walmart claims the system was de-energized by Telsa and showed signs of a fire after this with wires arcing at the time of discovery by Walmart. Tesla who is apparently monitoring these installs, got ground fault alerts between June 5 & September 11 2018 and failed to act or alert Walmart of the condition.
On the bright side, at least it was grounded in some fashion!!
248 also contains observations by Wallyworld's own consultant inspecting these systems. So far the best read.
249 has some interesting bits.
-Almost all the sites are 2016 and older, when Musk's cuz was installing these under solar city.
-Tesla also claims loss of power generation has cost them at least $13.7M and $37.4K per day.
-A list of recent non-solar store fires Tesla points out. $hit happens, man....
-Seems to state most of Tesla's issues with Wallyworld