Author Topic: AC Current variable trip circuit  (Read 9894 times)
Offline dan3460Topic starter
« on: November 27, 2015, 10:11:05 pm »
I'm looking for a circuit for my bench that will monitor AC current and it will disconnect when the current exceeds certain number. I will like to use this with my variac when starting antique radios and oscilloscopes for the first time. I have been using a dim bulb and keeping an eye on the ammeter.
So this circuit should be able to handle ac volts from 0-120V and current from 0-10A and it should have a button to reset the circuit when tripped.
I have seen a few that work on DC current, but I have not been able to find one that will work on AC.
Thanks for your help.
Dan
Offline dom0
Re: AC Current variable trip circuit
« Reply #1 on: November 27, 2015, 10:16:19 pm »
Outline: Two ~600-800 V MOSFETs source to source in the usual AC switch configuration. Gate drive e.g. with an ATX-SMPS base current transformer and a pull-down (see below!). Shunt & precision rectifier & average & comparator w/ hysteresis -> gate drive oscillator enable.
Problem: Making the circuit so fast, that it can disconnect w/o damage an instant dead short at 320 Vpeak is... challenging. Unipolar gate drive might not be enough ; you'll likely need <1 µs or even faster turn-off time overall.
I never built this ; having a variac with a quick responding analog meter is good enough for me.
« Last Edit: November 27, 2015, 10:18:40 pm by dom0 »
Offline TerraHertz
    • It's not really a Blog
« Reply #2 on: November 28, 2015, 01:20:55 am »
Funny, I've been thinking of the same thing since recently repairing something that had a snowball failure mode. Even using a variac at low output voltage, at some point the gear would overheat two diodes in its power supply causing one or both to short out, _then_ the mains fuse would blow. After that happened for the third time, I got sick of it. Had identified the fault, and fixed it, but it was annoying.
Such a 'fuse protector' needs to do more than shut off the power. Since it's intended for use with equipment open for servicing, it needs to fully isolate the mains once tripped. While still being fast acting enough to save fuses in the equipment, and avoid tripping the mains circuit breaker. (To save walking to the distribution board and resetting it.)
That needs an electronic switch (for speed, and able to take full short circuit current), in series with a double pole contactor (for isolation.)
For sensing, a torroidal current transformer. The circuit to set trip point and drive the switches would be easy,  I have suitable contactors and CTs, but I didn't decide on the electronic switch part yet.
Since it would normally be used between a variac (and possibly an isolation transformer too) and the equipment being debugged, it would have to withstand the load dump spike from the variac/transformer. So some big mosorbs on the input as well.
For ease of use it should have an analog mains current display, but a digital trip point setting, to allow just typing in a trip current. Plus a reset button, and a very visible "ON" warning light. And it would need its own separate power input, since the 'mains' it controls may be only a few volts from a variac set low. A 12VDC wall barnacle perhaps. Though the electronic switch part would require power rail(s) referenced to the mains.
Offline NiHaoMike
    • Facebook Page
« Reply #3 on: November 28, 2015, 01:38:12 am »
Maybe some large SCRs to crowbar the supply for the short time it takes for the input contactor to open? The isolation transformer is going to have some impedance that would limit the current and should be able to survive a brief short.
Offline dom0
« Reply #4 on: November 28, 2015, 10:49:53 am »
A COTS current transducer may be already to slow with maybe 0.5 µs group delay.
Offline T3sl4co1l
    • Seven Transistor Labs
« Reply #5 on: November 28, 2015, 10:58:00 am »
An electronic fuse isn't generally worthwhile because it's way too fast-acting.  It's also relatively expensive for the power level required.  You'll put in, probably about $40 worth of transistors, for your desired ratings, and only get a few microseconds worth of fault.  That's not long enough to charge capacitors during a turn-on surge (or perhaps even start warming up cold heaters!), or to reliably start a toroidal transformer (which draws a surge in the ms range).
A soft start would be good.  Perhaps switching in one, or a series of, resistor(s) before closing the circuit fully, and faulting out if any of those steps don't go well.
I've prototyped a lower rated DC fuse (40V 8A), but I've seen very little interest in it, so I don't know if I'll even bother to scale it up to line sized.
For simple solutions, it's hard to beat a handful of lamps!
« Last Edit: November 28, 2015, 10:59:39 am by T3sl4co1l »
Seven Transistor Labs, LLC
Offline Seekonk
« Reply #6 on: November 28, 2015, 04:16:48 pm »
I have an outlet with a number of parallel lamps in series.  I screw in more lamps for higher current.   I have used variations of this for 50 years in equipment repair.  Lamps increase in resistance when they heat up.  Typically have about 7 to 1 increase.  Anything normal won't light the lamp.
Offline NiHaoMike
    • Facebook Page
« Reply #7 on: November 28, 2015, 04:36:55 pm »
Or for an even greater fault to normal impedance ratio, use a capless (induction start) induction motor.
Offline Jeroen3
  • Embedded Engineer
    • jeroen3.nl
« Reply #8 on: November 28, 2015, 04:54:10 pm »
Like this: Tele Power G2IM10AL10 ?
But how fast does it need to be? uS, mS? Because shorts will be caught by a simple B class breaker and your ears. (the breaker will rattle if you slowly ramp up the voltage)
You can DIY if you'd really want to using a LEM module a relay and a comparator, but that does not meet the speed of a passive circuit breaker.
Offline DanielS
« Reply #9 on: November 28, 2015, 08:35:11 pm »
The turn-off is not too critical since you can add some series inductance to slow down current rise: 100µH at 320V peak becomes a very manageable 3.2A/µs short-circuit current rise rate. You can use RCD snubbers or even just some 20mm 200/400V MOVs (130/270 MCOV) to absorb the inductive spikes on break to avoid needing ridiculously high voltage MOSFETs.
Online Zero999
  • 0999
« Reply #10 on: November 28, 2015, 08:55:44 pm »
What about a fast current limit followed by a circuit breaker action if the fault persists for too long? For example, limit the current to 1A, if the fault persists for longer than perhaps 100ms then open the breaker. The trouble is the transistors need to be capable of dissipating the full fault power, until the breaker opens.
« Last Edit: November 28, 2015, 09:01:55 pm by Hero999 »
Offline joeqsmith
« Reply #11 on: November 28, 2015, 09:03:59 pm »
They do make mechanical ones.  The ones I have seen, you set the trip by adjusting the tension on a spring.
I did something like this when I made my last transient generator.   I just used a current sensor with an ADC hooked to a small microcontroller.  The software monitors the current and will cut the power if it gets above the set point (programmed from the front panel).   The isolation transformer I used is pretty small and limits the current to 500mA.
Offline DanielS
« Reply #12 on: November 29, 2015, 03:23:49 am »
I can imagine two relatively simple solutions:
1- use a thyristor or triac and progressively back off the firing angle starting from 179 degrees
2- use a motorized variac and start from 0V
Some loads might not appreciate being stuck in input voltage limbo or having odd input waveforms though.
A more complex solution would be a current-limited D-class amplifier.
« Reply #13 on: November 30, 2015, 01:59:37 pm »
I do understand that there are other ways to bring to power equipment under test, I actually use them. But my original question was to see if someone had a circuit or maybe someone can come up with a circuit. With DC is easier to make that kind of circuit, my problem is AC. The unit posted by Jerone3, I don't thing will be easier to control.
The circuit should do basically two things:
1- Have a knob where you can setup a tripping current, let say from 100mA to 10A.
2- Have a button that you can press an reset the circuit.
Besides the AC problem, this circuit will need to operate on variable AC as it should be mounted in front of a variac.
Offline Seekonk
« Reply #14 on: November 30, 2015, 05:58:55 pm »
I would use a 5A ACS712 with an additional shunt that can be switched in.  Then feed that into a UNO or mini328 and just drive a relay.  You will need a micro because of what you have wished for.  You will need delays, averaging, whatever to prevent all the false trips.  I've managed to get by for 50 years with just light bulbs in series.
« Reply #15 on: November 30, 2015, 06:12:31 pm »
Maybe I'm posting in the wrong board. I'm looking for a way to monitor AC current and then act upon a reference point. I understand, and I also use, a dim bulb, a wonderful idea. But at this point i'm more interested in learning if such thing can be done.
Offline dom0
« Reply #16 on: November 30, 2015, 08:00:33 pm »
It's totally impossible, since no one posted any hints, pointers, ... in this thread on how to implement it.
If you're looking for a schematic you just build (and not "I'm more interested in learning if such a thing can be done") then: No, I won't draw you a schematic. Do it yourself ffs.
« Reply #17 on: November 30, 2015, 08:14:19 pm »
Uhfaaa... Sorry to bother you.  :(
Offline Seekonk
« Reply #18 on: November 30, 2015, 09:01:52 pm »
Perhaps you should say what your intention is.  Are you looking for an approach based on peoples experiences or a fully tested schematic?   The latter isn't likely.  A micro is your best choice.  The ACS712 outputs 512 a voltage centered on 2.5V.  Run that into the A/D and look at values as fast as you can.    Subtract 512 and look at any positive number.  Do the same thing by subtracting the number from 512.  Any numbers over X trip the relay or add a filter to trip if say three of the last32 samples were high.
« Reply #19 on: November 30, 2015, 09:18:26 pm »
My intention is what I put in the OP. I was working on my bench and I thought it will be nice to have something that it will stop the current that you can set at a specific rate.
I was hoping for, as in other forums, that someone will post a circuit. Then someone else will criticize that circuit and post a "improved version" and so forth.
I'm a not a professional, I do this as a hobby.
Offline timb
    • timb.us
« Reply #20 on: December 01, 2015, 09:31:09 am »
Maybe *you're* that person.
Sent from my Tablet
« Reply #21 on: December 01, 2015, 12:56:30 pm »
Possible, my problem is that I have no experience with AC circuits. For example, to measure current in a DC circuit you could put a shunt low resistor and use a comparator to measure the voltage difference across the resistor, use that to drive a relay that will disconnect the output if it goes over a threshold.
How would you do that on AC? Can you do that on AC?
Offline dom0
« Reply #22 on: December 01, 2015, 05:11:41 pm »
Offline nfmax
« Reply #23 on: December 01, 2015, 05:34:13 pm »
Since panel mounting thermal circuit breakers are pretty cheap, you could always use a set of the things with different trip currents, selected by a rotary switch...
Offline timb
    • timb.us
« Reply #24 on: December 01, 2015, 08:45:12 pm »
A couple of posts above we gave you the answer. It's actually been mentioned at least twice.
Check out the ACS712, which is a Hall Effect current sensor. It outputs an analog voltage relative to the AC or DC current passing through. Sparkfun even sells a breakout board for it.
Other options include a current transformer.
Sent from my Smartphone