Author Topic: Data for ELEC-TROL 1980's solid state relays wanted  (Read 759 times)
Offline adinsenTopic starter
« on: July 14, 2026, 02:17:19 pm »
A frend of mine cleaned up his workshop and gave me some stuff including these four ELEC-TROL solid state relays. Two are marked type PEZ-2D00 and two PEZ-2D04.
They are date coded 8106 and 8110 so they are pretty old, but unused.
It says "input 3-18VDC" and output 240 VAC, but nothing about any current, power rating or insulation. Googling ELEC-TROL solid state relays shows up nothing.
He bought them for a hobby project in the early 80's while he was working for NASA in Huntsville. He later returned to Denmark, where he now lives near me.
I did some simple measurements on one of them: The input side draws 1.5mA at 3V. Testing the output side with a 12V DC supply doesn't show any connection depemding on the input. Ohming the output pins show a 1M resistance between them. They are obviously not designed to switch low voltages and uA currents  ;D
Judging by the size of them, they can probably switch a lot of current  8)
I hope someone might recognise them or could point me to documentation.
Online edavid
Re: Data for ELEC-TROL 1980's solid state relays wanted
« Reply #1 on: July 14, 2026, 04:12:52 pm »
Based on the model numbers, my guess is that these are 2A SSRs with zero crossing triac output.  If that's correct, they won't work with a DC load.  Try connecting an AC powered incandescent bulb or power resistor to the output.
The following users thanked this post: adinsen
« Reply #2 on: July 14, 2026, 06:55:01 pm »
Of course a triac circuit makes sense. 2A max rating seems very low. The PEZ-2D04 has a mounting bracket which I assume would double as cooling. A triac driving 2A will not get warm. The bracking is 2 1/4" (57mm) wide over the cooling tabs.
Thanks for the suggestion. I'll do some testing with it connected to the mains once I've made a safe setup for that :-/O
Online edavid
« Reply #3 on: July 14, 2026, 08:00:12 pm »
If you have a transformer, you can test it at a lower AC voltage.
Offline Zoli
  • Grumpy old men
« Reply #4 on: July 15, 2026, 05:38:20 am »
Considering the year(1981; 8106, 8110 date codes), I think 2A triac make sense.
Offline LaserSteve
« Reply #5 on: July 16, 2026, 10:26:34 am »
I used to be chief revision/design tech for a company that made legacy SSRs. Odds are that is a  2A or 4A triac. Expect high leakage currents from the legacy protective devices, in other words your modern low current LED lighting loads may or may not go full off,  or you may feel a tingle if you touch  the circuit, assuming its off.  (Not recommended)
Steve
"I calculated the stored energy, and it is enough to play the Dance / DJ Extended edition of "Baby Shark" in all 100 headsets for the production floor team simultaneously over 100,000 Times."
Well, I had to explain it to my boss, somehow.  He's an Accountant,  not a PHB.
« Reply #6 on: July 16, 2026, 08:17:55 pm »
Thanks all for your hints. Seems I've opened a can of "history of SSR's" here - interesting stuff  8)
I've done measurements with 23VAC from a transformer and a 250 Ohm load transistor. AC side is 50 Hz and the swiching is running 9 Hz. The first scope trace shows that the relay clearly does not have any zero detection, but otherwise works fine in this configuration.
Thanks for sharing, Steve! Inspired by your input I did another measurement, this time with a 12 kOhm resistor as load.
The second trace shows this. Clearly the relay works, but now we can see the leakage. I estimate the leakage current to be in the order of about 1 mA, if I read the trace correctly.
This makes the relays of limited use in a modern installation, but maybe I'll find use for them one day.
Thanks again all!
/Anders