I haven't read all the posts but the reason ac transmission is prefered over dc is that ac will go through a transformer and so, at the power station, they step up the voltage to 11kV or so using a transformer whose output approximates an ac current source.What this means is the current in the power transmission lines is tiny and relatively constant producing very low copper losses.When the electricity arrives at the houses,etc they simply transform it from 11kV back to 240V ac(U.K.) using nothing more than a transformer. So you see, dc transmission isn't viable.
A few things that you didn't get right about the UK electrical grid:
- Power is typically generated at a higher voltage than 11 kV (for example around 25 kV)
- It is stepped up for transmission across the national grid at voltages of 275 kV or 400 kV
- The output of generators and transformers is a voltage source--the voltage is regulated, the current varies with power demand
- The current in transmission lines is not that tiny; it could be thousands of amps
- Losses in the transmission grid are "low", maybe 2 - 3%, but this is still more than 1000 MW!
- The UK has several HVDC transmission links, to other grids in France, the Netherlands and Ireland
- Voltages in in the UK grid are based on multiples of 11 kV:
-> Transmission: 400 kV, 275 kV, 132 kV
-> Distribution: 132 kV, 66 kV, 33 kV, 11 kV
-> 11 kV is usually the last link in the chain before being stepped down to 240 V
The above is only a simplified summary of a large and complex system.