In the UK, for domestic consumers, EITHER the supply company provides an earth (TN-S or TN-C-S systems) OR it does not, making the earthing system entirely the consumer's responsibility (TT). Any Earth-Neutral bond on the supply side of the meter (TN-C-S), is the supply company's responsibility, as all the L and N terminals up to the meter are sealed with tamper-proof seals, so any such bond has to have been approved by the supply company before they applied the seals. OTOH there should *NOT* be an Earth-Neutral bond after the meter - the installation either uses the Earth as supplied by the supply company or the L and N *MUST* pass through a RCD and then a local Earth electrode system (TT) can be used (and in some cases - e.g. feeds to caravans & boats - is required even if the incoming supply offers an Earth terminal). This differs considerably from American practice where IIRC it is more or less standard to have an Earth-Neutral (or in American Ground-Neutral) link in the main panel, but it is prohibited in sub-panels or elsewhere downstream of the main panel.