Well the existing unit is it's own little hydraulic circuit. It is literally a hydraulic/mechanical user interface with an electrical switch. You turn a knob, this sets a needle, the pressure needle pushes another stationary needle up so if the pressure get to the set needle thy make contact. the needle that "remembers" the last high pressure stays in place. The reading in transmitted hydraulically from the force sensor up to the gauge. This all means that without involving electronics they had a visual on the set point and the current reading.
The machine itself does have a hydraulic circuit, so yes instead of finding an electrical load cell that will be quite expensive, we can use a pressure sensor instead in the hydraulics as the pressure does equate to the force. So 0-10V signal a potentiometer to compare to and it's fairly simple. The hard bit is the read out.
Turns out we have a Unitronics HMI+PLC knocking about, yes expensive solution, but this is a one off repair and we already have it.