I use liquidtight flex conduit for most HV (230v) runs in the industrial machines I wire up. One such machine has a large cast arm on bearings that oscillates about 20(?) degrees. I could easily bridge this joint with liquidtight--others have done it in the same application.
See the liquidtight at this joint (0:20):
https://youtu.be/3TQbhnDVqck?t=15
Is liquidtight designed to flex? I always thought it was flexible solely for ease of routing in environments such as this where rigid or EMT would be nearly impossible, but not for flexing. It's not so much the liquidtight as the conductors inside--are they at risk of work-hardening and increasing resistance and/or breaking?
I realize eevblog is electronics forum. If anyone knows a better forum to ask such questions, I'm all ears! (c:
Thanks.
I have not seen another forum which speaks of electrical wiring and conduit from a practical point of view, to answer your specific question. As far as the way that you have ran the flexible conduit, and yes Sealtite is a brand name, but there are others out there.
For moving parts on a machine, this is commonly used. I was directly involved in wiring industrial machinery as an electrician back in the 1980s and we used the same type of conduit for parts of the machine that moved. This was not only used for mains power, but more often there were control elements that needed wiring on moving parts as well, even though this may have normally been at 120 VAC potential, quite often we isolated these type of control signals with a small isolation transformer installed in the control cabinet.
For powering a unit or wiring up a control element such as a limit switch, we would use the flexible type conduit that you describe. However, we usually did not use individual stranded wire inside the flextite conduit, but a cable that had individual stranded wire would be used such as an "SO" (SO, SOOW) cable would be placed inside this moving flextite conduit. SO cable can be used in situations where it is not deemed necessary to armor the wiring if you did not require much protection, however when armor was required, the SO cable was ran inside the flextite where movement was involved. This reduces the chance of scuffing and abrading individual wire insulations with the added flexible sheath of the SO cable and it's underlying construction, which lends itself to flexing (i.e. multiple stranded twisted wires surrounded by twists of flexible material such as paper, cloth thread and other low stress materials). The twisted wires and materials used to construct SO type cable lends itself very nicely to control/power runs, even you do not use the flextite conduit for further armor protection. I would say that in many cases, the flextite is not necessary if you have used SO cable.
I have seen such units do many 10s of thousands cycles without any degradation of the copper or flextite conduit and/or SO cable. However, if you do this incorrectly, as some have said where you do not allow large radii of flex area, the mechanical stress will not only start damaging the flextite conduit, but, as also been said, work hardening the copper into a failure mode. The key is correct placement of fixed mounts, such as "P" clamps or "U" clamps.
I hope this helps.