There are reasons we need this PDU that I'd rather not go into. Originally, we wanted a switched AND metered one, but HPE said they didn't make one that would work with our power supply.
I'm wondering though, now that we know they make mistakes, do any of you guys see a Switched AND metered horizontal 2U PDU that will work with my 120-0-120 split phase?
You can't just change the plug out on the pdu that you have, you would have to completely change out all of the breakers and switching elements in side of it. Because it has to provide protection on both lines, not just one.
Changing the plug was talked about way back when everybody thought you had some mystery load.
A power distribution unit cannot be treated the same as a load, because it provides switching and protection.
As far as the multiple pdus goes you should have both of them running at the same time fed from different circuits obviously.
And then all of your servers that have redundant power supplies hook up one power supply plug into pdu number one and the other power supply plugged into pdu number two.
That way even if 1 pdu goes down completely your servers will still be running off the other pdu, as opposed to everything shutting down and you having to manually move things over.
Sent from my Moto x4 using Tapatalk
There are reasons we need this PDU that I'd rather not go into. Originally, we wanted a switched AND metered one, but HPE said they didn't make one that would work with our power supply.If HPE say that, they are saying they don't have a model that works in North America. That seems unlikely.QuoteI'm wondering though, now that we know they make mistakes, do any of you guys see a Switched AND metered horizontal 2U PDU that will work with my 120-0-120 split phase?You don't have a 120-0-120 split phase supply. You have a 240 V single phase supply.
Any PDU designed for the North American market that handles a 200-240 V AC single phase supply will work in your situation.
240v single phase North American.
That last bit is important when you're looking for stuff so you don't find something like you already have that's intended for Europe.
Sent from my Moto x4 using Tapatalk
208v single phase is a valid voltage in the US. In a commercial environment with a 3-phase Supply that is what you would get Line to Line.
But since it is not using all three lines, it is not a three-phase device.
Therefore it is a single phase device.
Sent from my Moto x4 using Tapatalk
See, I see things like 208V NA/JP with an L6-30P . That's gotta be a typo. It's single-phase. That must be a 240VAC North American one. But load capacity is only 5KVA. We're already over that.
It looks like the P9S15A is the only single phase option for switched and metered, and it is vertical mounting. It also only says on the specifications "200-208 V input". It doesn't say "200-240 V input". I do not know if 240 V would be a problem for it. HPE technical consultants would have to tell you the answer to that. If you talk to a salesperson they are likely to cover their ass and say "no"...
See, I see things like 208V NA/JP with an L6-30P . That's gotta be a typo. It's single-phase. That must be a 240VAC North American one. But load capacity is only 5KVA. We're already over that.
Why has it got to be a typo? I don't follow.
About the 5 kVA, that's a North American constraint, governed by the NEC.
If you have a 30 amp circuit the maximum continuous load permitted by the breaker and by the L6-30P is 24 amps. Now 208 V times 24 A is 5 kVA. That's the limit on one circuit, and since you would want one PDU per circuit, that's the limit on one PDU. (Since you have a 240 V supply the limit goes up to 5.7 kVA, but that's still your limit.)
So if your total system load is more than 5 kVA or so, then you need two or more 30 A circuits, and two or more PDUs. That's not only for redundancy, it is also an outcome of the National Electrical Code.
In summary, you can't put 7 or 8 kVA on one PDU, and neither would you want to.
Yes, but even the tech people I talk to say no, it's only for 208VAC. So it's listed as Single-Phase. Is it possible in the US to get single phase 208VAC?
Maybe modifying the current PDU would be the better way to go. A lot of work, I know, and it'd void warranty, but that just might be the best way to go about it.
Yes, but even the tech people I talk to say no, it's only for 208VAC. So it's listed as Single-Phase. Is it possible in the US to get single phase 208VAC?
Yes, 208 V AC single phase is a standard supply voltage in commercial premises.Maybe modifying the current PDU would be the better way to go. A lot of work, I know, and it'd void warranty, but that just might be the best way to go about it.
Bear in mind that if you do that you would have to install a 40 amp circuit to plug it into and you wouldn't have any redundancy. But other than that it might work if fitted with 2-pole breakers.
In a business environment every time you try to save money by not doing something correctly, Murphy’s Law gets reinforced big time. Granted there are degrees of correctness, but blatant disregard for tried and true power wiring is not recommended.
Things that you can get away with on the bench for short term testing seldom work out when put in service 24/7 unattended especially when it is your source of income.
You can’t afford pissed off customers, nobody wants a service that’s unreliable (even if it is cheaper than other options).
But what I was saying was could HPE make a PDU for 240V North America that provides a higher load using something like double-pole 40-amp breakers?
Now that many of us on this forum have spent countless hours advising Spork about powering his secret project, I would like to make a guess as to what this project might be.
My guess: Spork is turning his basement into a node for a VPN. If so, his revenue will depend on up time and throughput but the IT administrators want control of things like powering down servers and routing data. But a power outage won’t be the end of this business model because the customers can be automatically connected via another node. The VPN saves a ton of money by not needing to be located in expensive data centers plus they have a continuous tech on site. It could be a nice steady source of income that may grow. Worst case the VPN goes out of business leaving Spork with a sizeable investment not yet amortized.
Spork,
You need to stop stressing out so much and reflect upon priorities in life. Tell your wife and kids that you love them and thank them for their support; in other words try to turn the situation into the best possible scenario even if it isn’t fully what you want. I sincerely wish you the best with your project.