Hi Thanks for all the information.
I am trying to design a 5uH LISN based on your works which suitable for DC 200V situation. What should i notice when i choice the compoents and design the pcb ? I have browsed many scheme in the internet which based on your work, such as Wurth and LINEAR, the maximum input voltage is 60V. What should i do to improve the input voltage to 200V. Look forward to your reply.
Best Regard,
Hall.
The voltage rating is mainly related to:
1. Voltage rating capacitors across AC or DC power rail
2. PCB spacing
For capacitors across the rail, instead of 100V rating, suggest >500V, especially if you are connecting directly to mains. You can consider using X2 or Y2 safety types, or a 630 - 1000V rated normal film type.
For PCB spacing, spacing between line and neutral and between line/neutral to earth should be increased. A rather conservative value is around 7-8mm.
You should also consider adding a bleeder resistor (with proper power rating) across the input capacitors because 200V is quite a bit more painful/dangerous than 60V. If using with mains, add some fuses.
Hello TimNJ,
Thanks for your advice, that helps a lots. I have another questions as follows:
1. Could I use the inductance 744314110 when the Maximum DUT Current no more than 10A, no matter how high the input voltage is?
2. Where should I add the bleeder resistor? Parallel with the input capacitors such as C4 and C5 in the picture? What is the recommended resistance value of the bleeder resistor?
3. Whether the withstand voltage value of the components in the 10dB attenuator needs to be adjusted according to the change of the input voltage?
Look forward to hear from you.
Best Regard,
Hall
The inductors will not have much voltage across them. The voltage across the inductors is only caused by the DC resistance of the wire and some voltage related to V = L * di/dt. Generally, voltage breakdown (turn-to-turn) of inductors is unlikely, unless you are working with high voltages (>1KV), with something like a CRT flyback transformer. Don't worry about these inductors @ 200V.
Do you plan to use this LISN with AC? If yes, then do not use a polarized (electrolytic) capacitor for C5. Use a film type (polypropylene) instead. (The large blue/green capacitors in JayDiddyB's post above.) Depending on the standard, usually this capacitor must be 1-10uF, or thereabouts. This capacitors (or group of capacitors) should be rated 630V - 1000V, or use a X2/Y2 class capacitor(s).
The -10dB attenuator does not need to be modified, but C3/C6's voltage rating needs to be increased to work with mains. In the above photo, you can see 100nF film capacitor (probably rated 630V or 1000V). Most of the voltage is across C3/36, and only a small voltage is developed across R5/R13.
Add the bleeder resistors across C4/C5, yes. You can set the bleeder resistor to any value you want, depending on how quickly you want to discharge the capacitors C4 and C5.
http://www.learningaboutelectronics.com/Articles/Capacitor-discharge-calculator.php. Lower value of discharge resistor means faster discharge, but the power dissipation during normal operation will be higher. Suggest a power rating at least 2x the calculated power dissipation @ 200V/240V.